Could be sludge partially blocking the boiler HEX and pump impeller or/and pipework, system may require a power/chemical wash,was the inhibitor level kept up in the system?.
System design could be an issue - if you have unusually long runs on the backbone and it's split to 2 opposite ends of the property. Central heating should be so designed whereby most of the flow is performed by the larger backbone, ideally in a circuit or to a central location and then the radiator feeds are kept to similar lengths. If there are extended runs to larger radiators in 15mm then that can cause major balancing issues.
Was the system properly flushed, inhibited and a mag filter added? How clean is the system water?
I suspected as much… to my untrained eye it looks as though that’s been setup to be zoned… but I never did ask for that so I did think it was potentially non optimal running two unconnected parallel runs like thatWell yep, that layout is a bit of a mare - could have been made a lot more intuitive by connecting each of those 22mm's together creating a single looped circuit. If the current runs could be coupled without too much of an issue then that would probably go a long way to evening out the system. At the moment each run has quite disparate loads and being extended like that would always cause a major balancing headache. How large are the other rads, not the columns, on average?
Balancing that setup would require a long time to get it right. Especially if you have those 4 large triple columns right in the middle of the 2nd circuit.
A bit strange why the pump output was modulating at all on option 6 at a fixed constant pressure of 400mbar and also now at a far greater pump head and circ rate and rad output (if at the same flowtemp) that the boiler output is now only 30% vs ~ 40% previously.Found a solve for this eventually, incase anyone ever gets stuck with the same thing.
Had all the pipes inspected by a plumber, couldn't find a blockage anywhere or a wrongly connected pipe on the flow returns.
Had the boiler serviced and ruled out of any blockages.
Plumber suggested to me that perhaps the pump inside just wasn't strong enough, and suggested coming back in a couple weeks to fit an external pump to get the heat off the boiler quicker.,
That evening from fiddling around with the settings one last time before giving up, i noticed that the pump output % was modulating down alot, sometimes even as low as 30% even when I had it set to run at constant pressure (option 6 of 3-d1) of 400mbar.
I noticed in the manual if the pump is set to option 0 (the option where the pump is relative to the burner). It allows you to set a min and max % range for the pump output. So as a test I set the pump to max 100% (default) and min 80% (10 is default). And this has made a world of difference.
:-Outlet pipe and rads got hot to the touch within 20mins, even the triple column ones which usually take much longer.
:-Boiler modulated down to 30% after everything got nice and hot, and stayed at 30% for the remainder of the demand.
:- Delta between flow and return stayed at 20 for about an hour, it did eventually close to 13 but the boiler continued to condens. So assume this is fine albeit not ideal.
So it would appear the pump was indeed the problem, essentially being too lazy. Now i just need to work out whether I leave it setup like this, or run an external pump instead.
Yep… wondered exactly the same myself…. How can it be constant pressure if it’s modulating the output?A bit strange why the pump output was modulating at all on option 6 at a fixed constant pressure of 400mbar and also now at a far greater pump head and circ rate and rad output (if at the same flowtemp) that the boiler output is now only 30% vs ~ 40% previously.
You know that the boiler % output is quite accurate so at say a steady 30% output, 36*30%, 10.8kW and if the flow/return dT is 15C, then the flowrate is, 10.8*860/60/15, 10.32LPM. flowrate in LPM = kW*860/60/dT.
If the pump head increased from 400mb to 700mB then the increase in flow should be the flowrate at 400mb x a factor of Sqroot of (700/400), 1.32.
Its quite easy to calculate the flowrate as long as you have accurate flow and return temps, you said you were buying more accurate sensors?