Bonding conductors shall not be looped between services unless installed as a single continuous conductor.
Here's a better photo of the gas bonding I've found.
Hopefully that's acceptable for Octopus.
People have been talking about that alleged requirement for as long as I can remember, but I don't know where it came from.(This is something that interests me because I also have incoming gas and water that are near each other but remote from the CU. Do we know where this "continuous conductor" idea comes from?)
You can always connect the gas with the continuous conductor and loop to the water.
I thought that it had probably been made up by some old version of the OSG, but I can't find it in either my 17th ed. copy nor the current one, and it's certainly not in BS7671 (and I don't think ever has been). Is the infamous NICEIC (in one of its guises) perhaps responsible for having invented this one?
In any event, as EFLI has pointed out, if you're really concerned you could have a 'continuous conductor' connecting two or more remote extraneous-c-ps to the MET.
No.Am I correct in thinking that you are both suggesting using the same wire and looping through the gas earth point to the water one using a single cable to fulfil their single continuous conductor?
So the gas is already bonded with a continuous wire.If so I may have a problem doing that as in the last photo I posted the cable on the left comes from the CU and the one of the right goes to the water.
If you are wrongly told that it is not allowed to bond the gas pipe with anything other than a continuous wire, then bond the gas with the continuous wire and then connect another from gas to water.
Yes, as Octopus have confirmed, bonding not required.Looking at the photos of our supply pipe they look to be yellow plastic so hopefully that covers it anyway
They are even wronger than I thought, then.But he has been told that "Bonding conductors shall not be looped between services unless installed as a single continuous conductor"; it's not specific about gas.
These companies cannot make up their own wiring regulations.
I certainly was - and that is something that is often done (not the least because it is 'sensible').Am I correct in thinking that you are both suggesting using the same wire and looping through the gas earth point to the water one using a single cable to fulfil their single continuous conductor?
That is correct.namely that he seems to think that it is being said that the bond to the gas pipe must be 'continuous' but the bond to the water pipe does not need to be - and so has made a different suggestion.
Yes but I had assumed that neither the existing gas nor water bond was long enough to do that.Nevertheless, if one does as you and I have suggested, then that satisfied the perceived 'requirement', no matter how it is worded/interpreted.
Oh, I thought the myth applied to both.That is correct. I can only remember the continuous myth relating to the gas as it is somehow more important - or maybe water companies know there is no such rule.
That may, of course, be true. I was really talking, in general, about ways in which the myth could be satisfied, rather than specifically about the OP's (or endecotp's) situation.Yes but I had assumed that neither the existing gas nor water bond was long enough to do that.
I asked Octopus to clarify what they will accept for the gas bonding and they came back with the following.
Looking at the photos of our supply pipe they look to be yellow plastic so hopefully that covers it anyway however as the surveyor reported the earthing to be good on the gas when the earths were disconnected from the consumer unit I went looking for any bonding.
Using a snake camera I've just found that it is already bonded behind a cupboard where the supply enters the house using the cable that then runs on to the water stopcock.
View attachment 406758 View attachment 406761
It looks to me like the cable(s) is crimped to a ring connector and I'm not sure whether it is two cables that have been crimped together or one that has folded back on itself.
From the discussions earlier in this thread my understanding is that both should be acceptable as a single continuous conductor but I hope they see it that way too.
The cupboard is low down and has big drawers in it so I think I'll put a hole cutter through the back of the cupboard to make the joint accessible and to be able to get a better photo. I'll take care not to damage either the cables or the gas pipe mind.