Bonding conductors shall not be looped between services unless installed as a single continuous conductor.
Here's a better photo of the gas bonding I've found.
Hopefully that's acceptable for Octopus.
People have been talking about that alleged requirement for as long as I can remember, but I don't know where it came from.(This is something that interests me because I also have incoming gas and water that are near each other but remote from the CU. Do we know where this "continuous conductor" idea comes from?)
You can always connect the gas with the continuous conductor and loop to the water.
I thought that it had probably been made up by some old version of the OSG, but I can't find it in either my 17th ed. copy nor the current one, and it's certainly not in BS7671 (and I don't think ever has been). Is the infamous NICEIC (in one of its guises) perhaps responsible for having invented this one?
In any event, as EFLI has pointed out, if you're really concerned you could have a 'continuous conductor' connecting two or more remote extraneous-c-ps to the MET.
No.Am I correct in thinking that you are both suggesting using the same wire and looping through the gas earth point to the water one using a single cable to fulfil their single continuous conductor?
So the gas is already bonded with a continuous wire.If so I may have a problem doing that as in the last photo I posted the cable on the left comes from the CU and the one of the right goes to the water.
If you are wrongly told that it is not allowed to bond the gas pipe with anything other than a continuous wire, then bond the gas with the continuous wire and then connect another from gas to water.
Yes, as Octopus have confirmed, bonding not required.Looking at the photos of our supply pipe they look to be yellow plastic so hopefully that covers it anyway
They are even wronger than I thought, then.But he has been told that "Bonding conductors shall not be looped between services unless installed as a single continuous conductor"; it's not specific about gas.
These companies cannot make up their own wiring regulations.