Bidirectional and data sheets.
Unidirectional breaks the line pole supply side only. ... Bidirectional presumably breaks the line pole top and bottom
Any RCD obvious must break the connection between the 'line pole' on the supply and load sides, regardless of where the break occurs, so you are presumably just talking about breaking of the supply to the electronics?
Eliminates the TB problem and the issue of electronics staying powered via second supply on newer rcds.
I don't see "the issue of electronics staying powered via second supply on newer rcds" (after device trips) being an issue other than in relation to the 'Test Button problem' - and even that only becomes a problem if (I would imagine rarely) someone keeps the test button depressed for an appreciable period of time.
As I've said, this potential "Test Button issue" has always been there if people wired RCDs 'upside down'. If manufacturers had regarded that as an appreciable problem,they could presumably have addressed it. For example, I imagine that they could have included a diode plus a high voltage zener in series with the 'test resistor' such as to reduce the power dissipated in the resistor to a low enough value for a sensibly sized resistor (that could cope with continuous pressing of the button) to be used. Perhaps better, even if slightly more complicated, I imagine that it would have been pretty trivial to arrange for pressing the test button (even if it were kept pressed) resulted in a test current only flowing for a very brief period of time (e.g. by triggering a 'non-retriggerable' monostable).
Even just a slow-acting fuse (maybe 'fusible link') in series with the resistor might well be considered to be adequate.
2nd question Im not sure what you mean.
It really goes with the first question. The first asked what was the difference between unidirectional and bidirectional devices, and the second asked why these differences were considered necessary (i.e. what they were meant to achieve).
The old EM rcds were unidirectional and as you say bring supply in the wrong end you’ve got the potential test button issue
Yes - but, as far as my current knowledge goes, that's about "it" - i.e. the only problem I can see is the (minor, maybe even 'trivial') potential 'Test Button Issue'. In particular, and most importantly, I do not yet see reason why the RCD functionality of a traditional ('unidirectional') should be affected by current travelling 'in the other direction'. If there is any 'safety issue', the only one I can think of is the theoretical 'fire risk' associated with the test resistor overheating if someone kept the button depressed for a fairly long time whilst there was a net export.
Disclaimer; could be wrong on many points
Hardly needs saying - exactly the same could be true of me - we are, I presume, both human :-)
With the first raised problem with uni-directional we were told if it did not state load, input, or other on the RCD we could consider it as being bidirectional, so what is L? Is that load, line, or live? 1779027568645.pngSince in the main bus bars connect to the bottom I would assume it means line? I have seen boards with the RCDs either end, so the line would be on the other side, but since no earth connection, why would it matter which side is neutral, and which is line?
So 17th May 2026 so earlier to data sheet in question this Proteus data sheet says very clearly
so do we assume that Wylex is now a make to avoid? I see
the
to show bidirectional but looking at adverts for the RCBO I have fitted
the picture does not seem to show anything to show bidirectional, but adverts clearly say it is. I will assume the BD at the end of the part number shows bidirectional, it does say "After installation and testing of this product it is essential that the INSTRUCTION LEAFLET is available for reference" ups, I did not even notice a instruction leaflet came with it. But we will be called to many installations and need to know if bidirectional, we can't expect it to always be written on the device, or on the data sheet it seems. So is this a ploy to sell more consumer units?
Probably best to designate it to a Greek leter or three then we can all know what it is and the differences in definitions, hopefully theres still a Greek letter or two left for us to use in this situation.
Our Tutor on my first C&G Wiring Regs course course did comment that as Electricians we use Greek letters quite often. To enable us to charge more on our invoices - he might have been correct on that!
The bit of google research i did suggested the 2 issues. 1 internal contact will disconnect TB and second supply anyhow if so.
As expected most of the videos etc. don't really explain it fully.
As I said, given the current (unsatisfactory!) state of my knowledge, I don't see any potential problem other than the Test Button one (which is arguably pretty 'trivial'). Given that the electronics are obviously happy to be powered continuously (for years/decades in some cases), I can't see why it makes a jot of difference whether they remain powered after the device has tripped (breaking main connection between 'in' and 'out').
In the absence of any indications of 'in' and 'out' one would presumably have little choice but to treat it as 'reversible' ('bidirectional'), wouldn't one?
Nothing/no-one has yet told me anything that suggests that the RCD functionality of a device will be any different dependent upon 'which way around' it is connected. The only potsntialissues I've yet come across are those related to the Test Button.
Yes, the efixx video does as you say push the test button. They open it 1779095178174.png and show the three leg component has failed. The video says a year old. I did rewatch the video to see if it went in further, but no.
It did look at voltage optimizers, and I was surprised at that bit. To my mind the 253 volt limit is all part of the loss of PEN detection, and to use a voltage optimizer to stop it tripping just seems wrong, one is by-passing the safety features?
But as @JohnW2 has said, it seems to be a test button issue, and seems unlikely anyone would press the test button when in island mode. I very rarely press the test button, I have an RCD tester which seems a better option.
I have had problems with test buttons in the past, with a metal 10 mA RCD socket, where pressing it also took out the 100 mA RCD in the main board, so never liked the test button. Also found test buttons not working using a three phase RCD on a single phase supply, as they only connect to one phase.
There was a video by one of the efixx group where he used a plug and play solar, and he claimed with that, the solar switched off that fast with loss of supply (unplugged it) that there was no problem with reverse feed.
In general I consider with a TN supply the RCD/RCBO is added protection, and not really worried about type AC RCDs etc, as not really relying on them. If they fail to work, we have the same protection as in the 1960s, so no big problem.
But with a TT supply, the fitting of plastic water supply pipes, so we rely on earth spikes with a resistance of around 60Ω means we are relying on the RCD for protection, so with a TT supply RCDs are first line protection, and I would not want a metal consumer unit, although it seems we have no option any more.
Quite - which is why I have described the 'Test Button issue' as probably very trivial. It's only a potential problem IF the test button is pressed whilst there is 'export flow' through the device AND IF ALSO the button is kept pressed for an appreciable period of time after the device has tripped - and why on earth would anyone do that?
I may, of course, be wrong, but the more I see and think about this, the more I come to suspect that all this fuss about a 'requirement' for 'bidirectional RCDs' may really be unnecessary.
Yes, the efixx video does as you say push the test button. They open it View attachment 414888 and show the three leg component has failed. The video says a year old. I did rewatch the video to see if it went in further, but no.
I've just had a couple of watches of that video, and I have to say that I was a little surprised that, with 'reversed current direction', the test resistor clearly 'blew up' (with a bang and 'a puff of smoke') after a pretty brief period of pressing the test button. On reflection, I suppose that's not all that surprising - if designed to produce a test current of, say, 60 mA, that would amount to some 13.8W, which a 'small' resistor could only tolerate for a very brief period of time.
However, as you say, their experiment result in destruction of a component in the RCD electronics (rendering the device useless), which I can but presume that was the result of the 'test resistor' being (unnecessarily) very close to the device's electronics.
There are all sorts of ways in which this potential problem could be avoided, some of which I have already mentioned. Probably the simplest (which I don't think I mentioned before) would be to have an additional small pair of contacts which disconnceted the test button circuit immediately the device tripped.
Perhaps because simple solutions are possible, the guys in the video seemed to be suggesting that we would soon see a situation in which all new RCDs would be 'bidirectional' (i.e. without this test button issue) - so they may come to be regarded just as "RCDs" (rather than "bidirectional RCDs"), since nothing else will be available?
So are we thinking that "otherwise normal in electronics" idea that a resistor would be designed to be capapable of taking any conceivable current in "normal" usage and also any heating of an intensity able to damage nearby electronics was avoided by heatsinks or spacing dimensions, could be disregarded because the time this applies for in a correctly working (and correct polarity) RCD would render these considerations not to apply.
Therefore the fast operation of a fully functioning RCD need not apply?
Perhaps they never considered anyone wiring an RCD upside down or considered the instruction leaflet mitigates that risk suffuciently! We do now that in real life lots of people just do not read many instructions and just plough on regardless! We also might consider some people do actually read instructions but it`s easy to imagine some folk actually reading with due diligence time after time after time but eventually not reading the later versions or unfamiliar brands once they`ve done 20 or 30 or 200 or 300 etc (that can bring some complacancy even with the best of us).
If the manufacturer makes it clear from the labelling on the RCD of exactly which pole is which (as in both which pole is L and which pole is N and also which are the inputs and which are the outputs then we should see it).
Reminds me of a few years back I had asked for connection of two single pole isolators being required in an installtion, one was for Off Peak and the other for 24 Hour supply, I mentioned the possibillity of a bridge being placed between the two DP Switches as being a possible consideration of acheiving one means of total isolation for the whole installation (This one he countered - would the manufacturer endorse it?) and another possibillity of using a bog standard 3Phase (3 Ls and 1 N type) this one again would the manufacturer endorse it and the possibility a deliberate time delay between N & L swthing times (N being last to break but first to make) and would the labelling be all wrong anyway even if you applied your own labels over them they might be removed or fall off over time.
As it was I kept with the two single phase DP isolator ideas because, even if he sanctioned it then another inspector on another day might condemn it.
Reminds me a bit of what Ericmark mentioned with "Gas Engineers" stating non compliance of using a 13A plug and socket to isolate a CH system and only a SFCU would comply.
This is likely as we find they have loads of waffle in them. I bought a battery powered drill, grinder etc. Which does not come with batteries and charger, both sold as separate items with of course their own instructions.
So why with a battery powered device, are there instructions on how to fit a plug etc?
It is so clear these instructions have a cut and pasted section nothing to do with the product sold, they are likely included, so the manufacturer can say it was in the instructions in any court case, but there is so much waffle, no one will every read it.
Instructions from Ikea just have diagrams, no writing.
When I was an apprentice, going into the office and asking to read manual, regulations etc. Would be met with what do you want to know, and the foreman would tell you, you never got your grubby hands on the book.
The result was, we got things wrong. First book I got my hands on was the HGV MOT requirements book, I started as an auto electrician, and had to also do mechanics when no auto electrical work to be done. I remember us talking about what raves were, it was some part of the wagon which government gave a different name to than the trade used.
In collage, no internet back then, and a simple homework could result in hours in the library. One I remember was why does a lead acid battery voltage go down. Well as a mechanic we would just say because it is discharged, but as an auto electrician more was required.
I could find loads about other cells, but not lead acid. So I assumed it was similar, but when you think about it, not straight forward, as same chemical reaction start to finish. I still don't really know why the voltage changes.
flameport said:
Plug in items are not included and there is no way to know what people may choose to plug in.
If people choose to plug in undesirable equipment that causes problems, that is their choice and any consequences of that are their own responsibility.
This was to another thread, but similar subject. In the thread he answered talking about codes issued with an EICR.
Likely this is what is done. But done by the manufacturer.
I think the fly lead for the neutral and the single clamp one end for the line, stopped us using a single width RCBO the wrong way, however I remember with a Semens board, finding two types of MCB/RCBO mixed in the board, resulted in one switch to right for off, other switch to left, just asking for an error to be made. And double width and more units, often used in boxes which will allow with ease it to be connected either way around.
I still have, a never used, RCD from the 90s with no markings as to type AC, A, F, or B, and 4 modules wide, 30 mA likely before we filled them with electronics, with no Load marked on it, so would be very easy to wire up either way around, no way with its age I will find a data sheet, I had two in use in last house, and this was the spare.
So if I came across one in use, and trips within the times, then how can I justify a replacement? We see with cars, even 10 years old, being recalled as something has been found to be faulty. Like degrading of plastic in airbags, that dangerous that a do not drive recall was issued. To me if a RCD is likely to go up in smoke when supplying a socket circuit then there should be a recall. There should be a list by now, these RCDs are not bidirectional so we know which need changing.
My own consumer unit has 14 RCBOs (2 are bidirectional for sure) so 12 x £13.20 to £28.14 so between £158.40 and £337.68 for replacements which are type A double pole switching bidirectional. The old one, can't find data sheet, only the type A where mine are type AC although said type B on the box, but the diagram 1779182826924.pngclearly shows Load and Supply in so seems likely not bidirectional. I have 7 socket circuits, 2 use bidirectional, 1 could not be used to feed in as supplied direct from the inverter (EPS supply) 1 also supplies the cooker, so unlikely ever will have a reverse feed, and 1 supply North side of house, so unlikely to have solar plugged into it, so two socket supplies could if the house was rented have solar pluged into them. I know which sockets are bidirectional so I would not make the error. And since already have solar, not likely to add to it.
But the Wilex data sheet has no load or supply marked, there is simply nothing to tell one correct direction, just one L which is over one terminal so could mean line, in fact likely means line, as on the top, where in a consumer unit one would normally put the feed in, not the load. So if not bidirectional it is asking for errors to be made.
