reg 29The installer is required to leave the Installation Instructions and Benchmark logbook with the customer not take it away as I assume you meant by "but kept the paperwork"
Really rough workmanship, but the worrying part is the gas feed. It's connected to (original?) 15mm pipe. This is wrong unless the gas meter is really close. The other possible problem is the condensate pipe. it looks horizontal in the picture, but it should fall about 2.5degrees. Check the installation manual.
I would call them back the quality of workmanship is terrible, I think the bypass is to close to the boiler, most bypass valves are fitted a minimum of one meter away plus a gate valve is not the correct thing to use as a bypass. The condensate does not look correct and the gas pipe also looks wrong, you are ment to upgrade the system with trv's and a roomstat too, let me guess was it done in one day?
I am pretty sure that WB INSIST on at least 22mm minimum gas pipe to their boilers so that 15mm is going to blow any warrantee out of the window.
as has been said that is the shonckiest bit of work I have seen in a while and I hate having a go at another mans work but jaysus thats ruff
If it's not an optical illusion and the gas pipe does connect to that 15mm pipe then it is just plain wrong.. the pressure drop between the meter and the boiler has got to be more than 1 Mb.. I suspect that is why the price was substantially lower than the other quote. I hate pulling up floors to renew the gas supply but it has got to be done..
Having said that far too many customers think that I am trying to rob them when I say about the new gas supply...
Actually, another one had more recommendations, but was substantially more expensive
Why does that not surprise me - you pays your money & takes your choice.
The pipework really is not that bad!
People on this site love to be critical of all other people's work!
I would say that its about the average of what I see in London!
The only thing which is not right is the gate valve used as a bypass. It should have been a proper auto bypass valve but they cost about £20. Thats one of the results of not having a better installer or a fully itemised quotation.
As for the 15 mm gas supply. That is bound to be giving more than the 1 mB pressure drop allowed in the British Standard.
Some others hate me for saying this but you can call CORGI and ask them to measure the pressure loss and if they agree the loss is too great then they will serve a defects notice on the installer and require him to upgrade it at no further cost. CORGI visit free!
They used to require the drop to be no less than 1 mB but some inspectors are now accepting a mimimum of 18 mB at the boiler inlet if thats the minimum specified by the manufacturer.
I dont think yours will test as adequate if you have any 15 mm on the gas supply.
Tony
About that, I think it was properly tested but I will insist also when they come back. We checked that the gas supply from the gas meter is 22mm, so, without opening the floor, the guess was that it's 22mm all the way to the kitchen, then when the pipe "branch" to gas cooker and boiler (which should be about 1-2 meters from the boiler), it goes to 15mm.
Not bad Tony, It's Disgusting, I would have ripped the lot out.