A serious safety issue perhaps, but I don't see see how this argument can ever be resolved, because, IMHO, the 16th Edition contains contradictory requirements, viz:
If you choose to abide by the latter paragraph, then the requirements are met by the ordinary CPC in an ordinary RFC, as long as the terminations are made in a high integrity manner, i.e. never with two cut ends of the CPC under one screw terminal.
So which section of the 16th conveys the intended meaning of The IEE?
Even if there's a forum member who considers that sitting on a committee for a previous edition qualifies him to define the overriding interpretation, that isn't going to satisfy everyone here.
In 607-02-04 said:...shall have a high integrity protective connection complying with one or more of the following:
(iii) two individual protective conductors, each complying with the requirements of Section 543.
If you choose to abide by the former paragraph, then a high integrity "connection" (i.e. termination method) is possible only with the use of a separate, additional, CPC.But in 607-03-01 said:...the circuit shall be provided with a high integrity protective conductor connection complying with the requirements of Regulations 607-02 and 607-04. The following arrangements of the final circuit are acceptable:
(i) a ring final circuit with a ring protective conductor. Spurs...