What's wrong with a 1.5mm² cpc in a 2.5mm² multicore cable?
you still don't get it do you..
the "high integrity" is refering only to the fact that there will always be at least one path to earth from any given earthing point..
that is done either by
1. a cable of adequate size that it won't be easily broken by incidental damage
2. a cable of adequate size that is protected from incidental damage
3. 2 paths from each earthing point such that one path is still available should one path be broken through damage or failure of a mechanical termination.
it's this third one that makes radials comply if the earth at the final point is
a. connected back to the board
b. connected to the earthed metalic path of the conduit / armour feeding it
c. connected to the earth path of another local radial circuit.
this is already the case with ring mains since, as long as each cpc at each point is terminated independantly then failure of any conductor or mechanical termination still leaves every earth point on the ring connected to earth..
The regs say it does.Maybe but does it need to be increased anymore?
Because a radial does not start out with the same level of integrity in the first place.Surely if you needed 2 ring CPCs for a High integrity earthing RFC then why wouldn't you need the same for a radial circuit?
Well - that's one way of looking at it, and it could be so, but it does seem a bit of a stretch to interpret "This Guidance Note does not ensure compliance with BS7671" to mean "...because it only deals with a subset of BS7671" rather than "...because it is only guidance and not the official version of BS7671".The guidance note will not ensure compliance with BS7671 as it only covers earthing and bonding, none of the guidance notes cover the full scope of BS7671. Differing locations may also require different regulations to be met. It does however generally aid in explaining the aim of a number of the regs regarding earthing and bonding.
So basically the same wording as now.17th - not word for word but might help
543.7.1.3
The wiring of every final circuit and distribution circuit intended to supply one or more items of equipment , such that the total CPC current is likely to exceeed 10mA, shall have a high integrity protective connection complying with one or more of the following:-
(i) A single protective conductor having a cross-sectional area of not less than 10mm squared complying with the requirements of regulations 543.2 and 543.3
(ii) A single CPC of not less than 4mm squared complying with 543.2 and 543.3, the CPC being mechanically protected, eg; within conduit
(iii) Two individual CPC's each complying with section 543. The two CPC's may be of different types eg; metallic conduit together with a cable CPC. One of the CPC's may be formed by metallic sheath , armour or wire braid within the cable.
But with an interesting change?543.7.1.4 Where two CPC's are used the ends shall be terminated independently of each other................
When I read my copy, I see the words in black print on a white page "two individual protective conductors".BAS why do you keep saying that is what the regulation say - that is what you say that they say.
But earlier versions don't matter. Things change. Versions are replaced with later ones. That's why we are now working to the 16th/17th, and not the 1st.In any event my first post on this topic indicated that changes in the text may lead to confusion.
Lets flag up some of the errors in their text for you .
The problem starts with 607-02-04. It begins - The wiring of every final circuit and distribution circuit .... Thus including all final circuits.
Earlier versions specifically offered the standard ring main with appropriate modification as an ALTERNATIVE to 607-02-04.
Fit what? One individual cpc as is the norm on a non-high-protective-conductor-current ring final?However, all is not lost because I can make 607-02-04 (iii) para 2 fit, even if you can't.
Interesting how you regard changes to the regulations which damage your argument as "errors".This error is followed by the removal from 607-03-01 of the specific indication of permitted protective conductor size (1.5 mm²).
Au contraire - it makes the status of the conductors forming the ring cpc abundantly clear, because it clearly says it must comply with 607-02. And 607-02 clearly says that you must have one or more of:607-03-01 (i) makes clear that spurs must have a high integrity protective
conductor connection complying with 607-02 but it does not make clear the status of the conductors forming the ring. Note that the talk is of a protective conductor connection - it is not just about the protective conductor.
Now if you had argued that 1.5mm² could not be used and that 2.5mm² is required I could probably have agreed with you
Now 602 - take a close look at 607-02-04 (iii) paragraph 2 - ring circuit (4 * 2.5) + (2 * 1.5) = ?
However, I am at the CCU and I have two 2.5mm² conductor ends in the mcb terminal (or perhaps terminus) - so that is 2 * 2.5 = 5.
Next I go to the neutral connection bar and I remove the 2, 2.5mm² conductors related to my circuit. 2 * 2.5 = 5
Then I go to the earth connection bar and - you guessed it - I remove the 2, 1.5mm² related to my circuit. 2 * 1.5 = 3
Now I wonder what (2 * 2.5) + (2 * 2.5) + (2 * 1.5) equals - do you know?
The fact that I read what the regulations say rather than what they don't say does not mean that I don't understand the problem.but your take on this is frankly ridiculous - your interpretation of what is required does not make engineering sense and you would know that if you actually understood the problem.
FGS - don't be obtuse.If you remove one of the live wires from the breaker in the CU to the first socket in relation to which wire is removed then you end up with the sockets all still being live, so how can that be if as you say i've already removed the ONLY live in the circuit??
You still don't get it, do you..you still don't get it do you..
OK - so if 607-02-04 (i) means "the normal ring arrangement of a single cpc is OK provided it is a cable of adequate size that it won't be easily broken by incidental damage"this is already the case with ring mains since, as long as each cpc at each point is terminated independantly then failure of any conductor or mechanical termination still leaves every earth point on the ring connected to earth..
"Two individual protective conductors". If you think your version provides two individual protective conductors then please show us how you could remove one individual protective conductor and leave the other individual protective conductor remaining.This is a good summary. We might go further and include a description of the problem and the basic principles of the solutions. Note that many prefer the 'two path' solution over the 'more robust path' one.
"Two individual protective conductors". If you think your version provides two individual protective conductors then please show us how you could remove one individual protective conductor and leave the other individual protective conductor remaining.I will not say more at this stage - the comments made indicate that most understand it all anyway, and you BAS seem to think that you are in no need of guidance.
"Two individual protective conductors". If you think your version provides two individual protective conductors then please show us how you could remove one individual protective conductor and leave the other individual protective conductor remaining.This is a good summary. We might go further and include a description of the problem and the basic principles of the solutions. Note that many prefer the 'two path' solution over the 'more robust path' one.
"Two individual protective conductors". If you think your version provides two individual protective conductors then please show us how you could remove one individual protective conductor and leave the other individual protective conductor remaining.I will not say more at this stage - the comments made indicate that most understand it all anyway, and you BAS seem to think that you are in no need of guidance.