This is a reminder / explanation of the problem for anyone who may benefit.
Why do we need it - some types of electrical equipment cause a current flow to earth. This may be deliberate, as in the case of a low pass supply filter (functional earthing current), or just as a consequence of their operating characteristics (leakage current).
The cause is not really important here - it is the fact that this current flow exists that is of concern.
Just a word or two on the magnitude of the current - we become particularly concerned when currents of 10mA or above might flow. This concern has nothing to do with the current carry capacity of the circuit protective conductors (cpc) - they can easily carry more than 1000 times 10mA.
10mA is based on shock protection data - in particular the 'let go' threshold for the average person. If a current of 10mA (ac) or more pass through your body muscle contraction may prevent you from 'letting go' or breaking free.
How does the hazard occur - if the cpc path is broken then the current flow must stop, however, the potential for the current flow remains and this manifests itself as a potential difference on any class 1 (earthed metal case etc.) appliance that is downstream of the break in the cpc.
So what - I here someone say
. well we now have a potentially lethal shock risk (the actual current flow may be greater than 10mA) and it has occurred because of a SINGLE failure in the system.
Contrast this to the series of events necessary to be in the same position for a class 1 appliance without these standing earth currents.
ONE we need a fault to occur within the equipment that cause the metal case to become live. TWO we need the normal shock protection measures (usually EEBADOS) to fail to clear the fault within the specified safe time and voltage limits. (You see I can count
).
So we got into all this trouble because of a SINGLE failure in the system. We want the TWO fault tolerance of the normal system so how might we achieve it - well in the case of a radial circuit we could simply provide a SECOND route to the means of earthing by adding a cpc. The ring circuit already has TWO routes so we don't need another, however - for both ring and radial we do want TWO independent terminations for the TWO routes to the means of earthing. Hence the socket outlets with two terminals and the instructions to use two terminals at the DB.
This was often called duplicate earthing. There are other methods, such as using larger conductors for example, which seek to use more robust connections that are less likely to fail.