Hi all. Just to see your opinions on this.
Started work on a local authority housing job. Wiring showers in highflats.

The spec is 2 way rcd enclosure with 40a mcb and the other way blanked off.
We are to use 10mm tails into henleys. 25mm tails in use for cu and 100a main fuse.
I say we should be using 25 as its 100a cutout. But foreman says its ok as it wont pull more than 40a.

I would agree with him if it was a 40a stand alone rcbo only. But the extra way leaves it open for they 10mms to be overloaded.

Thoughts please
 
Sponsored Links
Do you need a busbar, surely a 10mm link from the Rcd output to the Mcb would be neater
 
Use a 3 module enclosure? Though there weren't too many about last time I needed one.
 
Sponsored Links
A 2 pole 40A RCBO would be ideal.

Not likely the 10mm will be overloaded even if another circuit was installed, 10mm singles are rated to about 65A.
 
Use a 3 module enclosure? Though there weren't too many about last time I needed one.
Isn't that a "shower consumer unit"?

The one in the OP must be a "garage consumer unit" so probably won't work for showers. I suppose I'd better add a smiley. :)
 