1mm Radial spuring off...

Joined
31 May 2005
Messages
9
Reaction score
0
Country
United Kingdom
Hi. Is it ok to 'star' off from an already 'stared' radial lighting circuit? For example: one feed into a j.b going to two other j.b's each having their own lights on (one feed being split into 2 then those two being split again further on down the line).

Thanks.
 
Sponsored Links
Assuming that all of the accessories are the correct current rating and have the correct British Standards and that safety is not compromised and it installed to BS7671 and complies with the Building Regulations then yes it is acceptable.
 
jonathan.hancock said:
Hi. Is it ok to 'star' off from an already 'stared' radial lighting circuit? For example: one feed into a j.b going to two other j.b's each having their own lights on (one feed being split into 2 then those two being split again further on down the line).

Thanks.
yes

a radial is a long branch. you can take more feeds from it. just make sure you use the same size cable as what the existing radial is wired in
 