Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.
Are you talking specifically about 3C+E (in which case I would probably agree with you) ?
1.5 mm² T+E certainly has good/valid purposes in a domestic property (fused spurs/branches from ring/radial final circuits, 16A circuits {e.g. immersions}, many 20A radials etc.) - in which cases it is cheaper and uses less copper resources than does 2.5 mm².
I certainly agree that 1.5 mm² cable on 5A/6A lighting circuits has never made any sense, and I really don't understand why/how it ever became fashionable!
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local