A generator for future powercuts

Joined
12 Feb 2015
Messages
705
Reaction score
25
Location
Surrey
Country
United Kingdom
I was thinking, THEORETICALLY, a medium size (6kW) diesel generator (DHY8000SELR Hyundai), which I would hopefully run on heating oil (about £1/lt for 1000lt).

I would place it either outside, or maybe in the basement. In the basement I would need to think about exhaust and clean air intake and CO etc - but it would not annoy the neighbours. But for fire hazard and possible fumes, better have it outside.

I would disconnect the house from the mains (I already have a CED SD100 isolator). Then I would plug it in a normal house socket.

My earth connects to the neutral of the network at the meter. Would I need an new earth rod? I am not sure if the generator provides an earth and/or requires its own earth. Also I am not sure if there was some serious network fault, would the neutral still provide an earth? What if the neutral also got disconnected?

If I connect it to a wall socket, how would the fuseboard's RCD even work?

I could connect it to the external CED SD100 isolator (get a new isolator with 2 positions maybe) and then feed the house that way. Then the house would not know the difference and the various RCDs would all work as normal.

Is this a good plan?
 
For the consumer unit to be supplied with a commando plug, which you can select if plugged into a generator or DNO supply would work, but it has a big draw back, one is it is manual, and two you would have nothing to tell you when power returns.

So in the main we are looking at only part emergancy cover, so you can see when the power returns, and some automated change over when power fails so items like freezers don't defrost.

Also earlier this year, road fuel duty was added to 35 sec gas oil used in generators. Not a clue why, as to 28 sec gas oil and a TVO engine not sure.

But I think you need to consider it more carefully.
 
But I think you need to consider it more carefully.
I have just read one similar thread from 2022, talking about a generator in a shed.

In case of a powercut, a fault, if the N of the supply has also gone down, my house Earth would now be relying on random, incidental earthing points, like water pipes inside walls and soil, here and there (mains water and gas are plastic).

This dodgy Earth would not be a problem, until you tried to install a generator.

So the generator, the whole machine and its casing, has to have a good earthing rod nearby and must then provide the Earth for the house?
 
The earth problem is a real headache. We often have no idea where underground services run, so an earth rod which is close to a metal water or gas pipe, may not be a true representative of true earth polarity. And in general we want around 3 meters separation between earth systems, so we tend to just add earth rods to the orignal and cross out fingers that if there is a loss of PEN that the earth will not drift from true earth enough to cause a danger.

My own house has a single rod under the rear patio connected to the DNO earth/neutral, and it would be enough if the DNO earth completely lost, and bad enough that if the whole of the PME system remaining tries to earth its self through it, the current would be limited to an acceptable level.

When working on the gas plant at point of aye, the DNO earth and site earth were connected through a huge resistance around the size of a small car, to limit the current in the event of a fault.

I saw with a radio ham, with an earth tape around his garden for the transmitter, the earth wire melt when the DNO supply lost its PEN connection, there are rules, but it seems they are often ignored.

The local heritage railway has taken over a building which was originally start up units for local businesses, as a result it has 4 independent supplies, all with their earth bonded to the metal frame building, and with air lines, connecting it to other buildings, which in turn is connected to 8 miles of railway line, when an EV charger was installed, they fitted an earth rod, with so much metal in the ground, one has to ask why?

Maybe I am an unusual electrician, working in Algeria and Falklands we did not have a local supply, I looked after the generators as well, with Hong Kong the supply to site was 11 kV transformed down to 10 kV for the TBM and further down to 660 volts for main motors, and 220 volt IT supply for the control cabin, some of the Falklands supply was 3.3 kV I don't have a high voltage ticket, but have worked with it, and as a radio ham also earth was of interest.

So I know enough to realise how little I know, its not easy by any stretch, which is why I think plug in solar should have never been allowed. But I could write pages and pages about earthing systems, good enough to say its not really a DIY job.
 
Agree with the others – please don't backfeed through a socket. You'd need a lead with a plug on each end, and the pins go live. If the main isolator is ever left on, you're also putting power back onto the network.

If you go the generator route, get a proper changeover switch fitted between the meter and the consumer unit. Then the house can only ever be on one supply. Your electrician can sort the earthing at the same time. On a PME supply, the generator normally wants its own earth rod when it's running on its own, so your RCDs still do their job.

It's also worth pricing up a home battery with backup power (EPS). It switches over by itself in a power cut. There's no fuel to store and no fumes. It won't run the whole house like a 6kW genny. But it'll keep the boiler, fridge, lights and router going. If you have solar, or are thinking about it, the panels top it up during the day.
 
I was thinking, THEORETICALLY, a medium size (6kW) diesel generator (DHY8000SELR Hyundai), which I would hopefully run on heating oil (about £1/lt for 1000lt).

I'm pretty sure you may use red diesel, if you can get hold of any. Friendly farmer nearby?
 
So the generator, the whole machine and its casing, has to have a good earthing rod nearby and must then provide the Earth for the house?
No.

The generator provides the earth for the installation.
An earth electrode or similar is required to provide a reference to Earth, so that RCDs will operate in the event of a fault.
 