However, with overhead ABC, or underground, cables I would imagine that selective loss of the neutral conductor is extremely rare.
Remove "extremely" and I would agree.
However, with overhead ABC, or underground, cables I would imagine that selective loss of the neutral conductor is extremely rare.
As I interpret this post it is a good reason to not import the DNO's earth and not bond the DNO's neutral to the customers earth.Investigations revealed the blast was caused after a piece of cable was cut from an overhead line. This affected the earthing of the electrical network in the area and resulted in some unusual electrical activity, which affected some of the gas pipes within the properties. This resulted in the fires and explosion.
Yorkshire Post Saturday, 11th February 2012,
Initial fires were caused by overloaded Main Bonds to metal water mains,
Do you know anything at all Winston? It certainly appears to me that you don't.
I'd have though by now you would have learnt that I have a lot of experience and can identify and test most circuits with a reasonable degree of accuracy and by now.
As I mentioned earlier there is an excellent log book for the building which the customer encourages the use of as a note book and there are several sets of dead tests showing ~0.35Ω of L & N end to end resistance and my first thought at 11pm on a callout in the cold and damp was Winstons repeated and incorrect bleating so I just had to do this:View attachment 203839
So once and for all will you PLEASE keep your factually incorrect and rude/arrogant statements to yourself.
I find it so sad that while dealing with potentially life threatening situations one of the first thing that goes through my head is the comment from a silly little know nothing.
I have always been under the impression a TT earth is never connected to an imported earth, we had major discussionsYes, I'm also a bit uncertain as to what SUNRAY meant. As you say, the 'M' of the 'PME' (which is required with TN-C-S) means that there are 'multiple' connections between the supply neutral and earth electrodes (even though, if what westie used to tell us is correct, that 'multiple' often/usually meant only one 'earth' in addition to the one at the transformer).
Furthermore, it was only at the 11th hour that the requirement for all TN-C-S installations to have a local TT rod (connected to the TN-C-S 'earth') was removed from the draft of the current version of BS7671 - so I presume that this was not considered to be a 'hazard' (which sounds reasonable, since hardly any credible domestic TT electrodes would have a low enough impedance to result in enough current to flow to damage, let alone 'set alight' any credible cable).
In practice, main bonding cables from TN-C-S 'earths' to low-impedance extraneous-c-ps, are far more likely to carry very high currents than is a connection to a domestic TT electrode.
Kind Regards, John
Trolling again! Go back to the Screwfix forum...OK so this was wired unconventionally. I will rephrase my statement:
Lights are not normally wired on rings. I'm surprised you think these are.
Are you going to remove the return wire to save confusion later?
Ring final circuits have been conventional for well over half a century.OK so this was wired unconventionally.
Thank you for admitting you are wrong yet again.I will rephrase my statement:
Lights are not normally wired on rings.
Working on lighting rings is not actually that uncommon.Lights are not normally wired on rings. I'm surprised you think these are.
Why on earth should I?Are you going to remove the return wire to save confusion later?
Ring final circuits have been conventional for well over half a century.
In many countries it is compulsory and, as I said, it was only at a very late pre-publication stage that the requirement of a TT earth for all electrical installations in the UK was removed from the final draft of the current version of BS7671.I have always been under the impression a TT earth is never connected to an imported earth, we had big discussions
You mean the DNOs (local) distribution network? If so, they surely can't allow that situation to persist (if it's true), can they?I did manage to speak with the crew on site earlier this afternoon who have said there were no earth connexions in their network due to metal thefts.
Well, even if it's left there, the word is obviously open to a wide range of individual interpretations; we're real back to the 'risk perception' business again!Remove "extremely" and I would agree.
All agreed (and, despite your modesty, the 'patchwork' is fairly impressive!).Quite right, it may have been noticed all the breakers in the CU are off and aqequate testing for dead was performed. Not importing the DNO's earth into the building would have removed so much danger, as would not exposing within the building. This would effectively negate any percieved requirement to use a device to disconnect anything. Excuse the patchwork but a basic version of a nicer way to put this SWA in:
In case anyone doesn't know, or has forgotten, the text in red in the following was present in earlier drafts of BS2761:2018, but did not appear the the final draft, which is what was published as the current regulations (BS7671:2018)...In many countries it is compulsory and, as I said, it was only at a very late pre-publication stage that the requirement of a TT earth for all electrical installations in the UK was removed from the final draft of the current version of BS7671.
One of the practical problems that was extensively discussed when we thought it was going to become a requirement was the potentially dangerous situation that can arise, temporarily, when some, but not all, properties using the same part of a distribution network have their TN earths connected to local TT ones.
The penultimate draft of BS7671:2018 said:542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3, as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2. Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to Earth.
Anyway, whatever adjectives one uses, I would have thought that only extremely improbable circumstances could result in the N conductor, but not the L one, of an ABC cable or an underground multi-core cable to become 'broken'.
Indeed not, and they quite rightly they isolated the sub within minutes of being on site.You mean the DNOs (local) distribution network? If so, they surely can't allow that situation to persist (if it's true), can they?
Kind Regards, John