Reminds me of a fault I went to a while ago, TN-CS supply to a farm cottage type property (no outbuildings, not farmhouse, just a worker's cottage), reported issue was no hot water and getting shocks off pipework, the no hot water was quickly ruled out as conincidental, the thermostat on the immersion was faulty, seemed the contacts had been high resistance overheated a bit and managed to become either open or very high resistance (I cant remember), but anyway it had no bearing on anything else.
Zdb was approx 0.20ohms, switched off, disconnected main earth and did the test to incomming earth... still much the same. Went to put earth back in the CU and it arced a bit, thats not right, left it out for a moment, put a temporary earth electrode in the front garden (long drill bit), wander lead back into the house, tested between lead and earth bar in CU, nothing, tested between lead in DNO earth and got about 193v (fluctating slightly). I must admit I never thought about putting a lamp across it. Put a call into the DNO while drove back to town to get a new immersion stat from the wholesaler. Got back and found the DNO chap was already on site* and had verified the fault existed and was scratching his head and making phone calls
*I got a call back from what seemed to be a supervisor, who must have seen the ticket and wanted to confirm that I was reporting a PME earth to ground voltage of 193v, not a phase, neutral voltage of 193v and seemed to prioritise the call following this.
Sunray, does it look like this installation is off a smallish transformer which supplies only a very few customers?