Inside the cabinet where my fuse box is located there is a fused spur which feeds an alarm control panel. The fused spur is connected to a 6A MCB, there is nothing else connected to the MCB.

I want to run 1 single socket ( located inside the cabinet ) and 1 double socket ( located outside the cabinet ) from the fused spur.

The sockets would be used for a telephone charger and two small lamps.

Havn't got round to looking yet but I assume the fuse in the spur is 3A.

Does this contravene any regulations.

Any advice, better solutions most appreciated.
 
Sponsored Links
It should be OK, provided each socket is labelled as "Max 6 amps only", and is run straight from the B6 breaker - if on the ground floor - it must be off the RCD side of the board,. Use 1.5.mm cable for each socket (can handle 16 amps max), in case someone tries to swap it for a B16 breaker.
 
The best would be to run a separate circuit for the sockets if possible.

If not possible I would create a radial circuit using 2.5mm2 T & E cable and 20A MCB (in place of the 6A MCB). The FCU will be part of this radial. I would connect the alarm to the load side of the FCU and change the 13A fuse in the FCU to 3A.
 