If the cable is not up to carrying 10amps then it is not wise to fit one.
certain factors dictate what the cable can safely carry.
Bigger breakers may sometimes solve problems like yours.
But can sometimes create other potential hazards,unless the circuit is checked first.
These checks may have been done by the electrician ,hopefully, so dont worry
Without checking the book, I am not sure whether a B10 is any better than a C6 regarding your tripping case
B breakers are more common in domestic as they trip faster,
As you say the board is sensitive.
C breakers are more commercial use as they trip slower, but as said by others , the Earth Loop Impedance needs to be lower for them to operate.
To jump from B to C the max limit for the ELI is reduced,
To jump from 6 to10 the max limit for the ELI may be further reduced.
The cable size will also need consideration
That is why they are asking for the ELI to the light.
The ELI readings you gave are for other things.
certain factors dictate what the cable can safely carry.
Bigger breakers may sometimes solve problems like yours.
But can sometimes create other potential hazards,unless the circuit is checked first.
These checks may have been done by the electrician ,hopefully, so dont worry
Without checking the book, I am not sure whether a B10 is any better than a C6 regarding your tripping case
B breakers are more common in domestic as they trip faster,
As you say the board is sensitive.
C breakers are more commercial use as they trip slower, but as said by others , the Earth Loop Impedance needs to be lower for them to operate.
To jump from B to C the max limit for the ELI is reduced,
To jump from 6 to10 the max limit for the ELI may be further reduced.
The cable size will also need consideration
That is why they are asking for the ELI to the light.
The ELI readings you gave are for other things.