pbar said:
Why is that?
Why will a 13amp fuse not blow when 40amps are drawn?
Is it because it will only be brief
Yes its because its only drawn for a short period. In many circumstances a 32 amp MCB will trip before the plug fuse does. In heavy faults, for example a short circuit, many hundreds of amps are drawn briefly. This instantly trips the fast magnetic trip in the MCB but the plug fuse is usually unharmed because the MCB is so quick at clearing the fault.
Many fridge freezers have larger compressors. Our new one is quite loud when it starts, and the lights go dim for a second, like when someone turns the 9kw shower on!