Arcing sound from plug socket switch

Joined
3 Jul 2010
Messages
81
Reaction score
0
Location
London
Country
United Kingdom
I have a double socket in the bedroom and every time I turn the switches off for the tv I can hear a arcing noise from one of the switches so I plan on changing the socket but is it best to use a single or double pole socket and what's the best brand to buy.
 
Sponsored Links
Joined
30 Jun 2009
Messages
21,627
Reaction score
2,567
Location
Londonderry
Country
United Kingdom
It does not really normally matter whether you use SP (single pole) or DP (double pole). But in theory DP would be safer.
I use BG or click normally. But MK, Crabtree etc.. are fine.
 
Joined
11 Jan 2010
Messages
7,607
Reaction score
606
Location
London
Country
United Kingdom
TV have their own switches so why are you turning the socket off? But if you must turn off the TV first. A new socket may do the same.
 
Joined
3 Jul 2010
Messages
81
Reaction score
0
Location
London
Country
United Kingdom
TV have their own switches so why are you turning the socket off? But if you must turn off the TV first. A new socket may do the same.
The tv don't have a switch so I have to put it on standby then turn it off at the socket.
 
Joined
27 Aug 2003
Messages
69,757
Reaction score
2,884
Location
London
Country
United Kingdom
I have a double socket in the bedroom and every time I turn the switches off for the tv I can hear a arcing noise from one of the switches so I plan on changing the socket but is it best to use a single or double pole socket and what's the best brand to buy.
Have a look and see how long the cables are behind the socket, and whether there's any slack that can be pulled through. Maybe post a photo.

Reason being that if they are very short and there is no slack then you might need to make sure you buy a socket with the terminals in the same places as the existing one if you are to be able to connect the wires.
 
Joined
3 Nov 2006
Messages
26,582
Reaction score
2,812
Location
Bedfordshire
Country
United Kingdom
socket switches are able to make and break full load current.

For most makes that is true but only for non-inductive loads.

From the tech spec for MK plate switches "" Current rating: 20 amps – no derating when used on fluorescent or inductive loads""

The same "no derating" comment is not applied to MK 13 amp sockets
 
Joined
28 Jan 2011
Messages
50,100
Reaction score
3,350
Location
Buckinghamshire
Country
United Kingdom
The same "no derating" comment is not applied to MK 13 amp sockets
I might, of course, be wrong, but I would be rather surprised if BS1363 allows a switched 13A socket to have a switch which is not able to safely (and without damage) break a highly inductive 13A load. Does anyone know?

Kind Regards, John
 
Sponsored Links
Joined
27 Aug 2003
Messages
69,757
Reaction score
2,884
Location
London
Country
United Kingdom
upload_2018-9-30_17-11-53.png

upload_2018-9-30_17-13-0.png
 
Joined
28 Jan 2011
Messages
50,100
Reaction score
3,350
Location
Buckinghamshire
Country
United Kingdom
Interesting. Thanks. I suppose the requirement for it to be able to break a "substantially non-inductive" current of 17A, means that it would able to break an "appreciably inductive" (but not necessarily 'highly inductive') one of 13A.
 
Joined
27 Aug 2003
Messages
69,757
Reaction score
2,884
Location
London
Country
United Kingdom
Dunno.

Or an extremely inductive load of a couple of amps? It's a TV power supply remember..
 
Joined
28 Jan 2011
Messages
50,100
Reaction score
3,350
Location
Buckinghamshire
Country
United Kingdom
Indeed. In any event, I think that most SMPSUs have PF correction these days, so probably not a significantly inductive load at all.
 
Joined
11 Jan 2010
Messages
7,607
Reaction score
606
Location
London
Country
United Kingdom
The tv don't have a switch so I have to put it on standby then turn it off at the socket.

Why? It will miss all the overnight updates. Modern TVs take negligible power in standby and are meant to be left in standby to receive the updates. Most countries don't have switches on their sockets.
 
Joined
3 Nov 2006
Messages
26,582
Reaction score
2,812
Location
Bedfordshire
Country
United Kingdom
It is not the magnitude of the current being broken but the magnitude of the stored energy on the inductor when the current is broken and the back EMF created when the nagnetic field is collapsing. The resultant arc between the switch contacts is the main cause of contact wear and premature failure when supplying inductive loads
 
Joined
28 Jan 2011
Messages
50,100
Reaction score
3,350
Location
Buckinghamshire
Country
United Kingdom
It is not the magnitude of the current being broken but the magnitude of the stored energy on the inductor when the current is broken and the back EMF created when the nagnetic field is collapsing.
Yes, but that's really just a play on words, since the 'magnitude of stored energy' (stored in magnetic field) is, itself, determined by the magnitude of the current.

In fact, since that stored energy is given by LI²/2, the fact that it is a function of I², rather than just I, means that the stored energy increases rapidly as current increases.

Kind Regards, John
 