• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Bathroom Extractor Fan

Joined
12 Jan 2010
Messages
35
Reaction score
1
Location
West Midlands
Country
United Kingdom
Hello there.... Looking for a bit of advice, regarding fitment of an extractor fan in a bathroom..... at present we have an extractor fan (exterior wall mounted), pull cord operated type,which is being fed from a switched fused connection unit, which is situated inside the bathroom..... approx 75mm, below the ceiling level.......
1. is this ok?..... or does it need to be an unswitched type?
2. The whole installation is being fed to the fused connection unit from a socket outlet, in an adjacent kitchen, in metallic conduit, buried in the wall/plaster...... this is an old system, which is not protected by a rcd..... I know its in a bathroom, but if its supplied by wiring "inside" the metallic conduit...... does it need it?..... Many thanks.
 
The FCU has to be suitable for the environment using an IP65 unit it would be but since we don't know what the FCU's manufacturer recommended this can't be answered and also we don't know what zone it is in.

All items in a bathroom now need RCD protection but you don't need to upgrade it is not retrospective.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top