baxi 100 he co readings

Joined
8 Sep 2005
Messages
2,539
Reaction score
665
Location
worlds end
Country
United Kingdom
baxi/potterton condensing boiler co and co2 readings ok on high rate ,gas rated all ok standing and working pressures ok ,problem is as boiler starts to reach temp and fan slows co reading goes way up ,boiler has had new burner ,sump and condensate clear,flue ok , any ideas?
 
Sponsored Links
You don't say whether this is the 100 HE conventional boiler or the 100HE Combi. It sounds like the minimum differential ratio is out of calibration.
There is no procedure for getting the boiler into minimum rate or way of checking the gas/air differential on either of these.
m.i only give CO/CO2 readings for maximum
Fan speed is definitely slowing when C0 figures start to raise?
 
Com box door seals showing any signs of damage-ideally changed annually. Although I don't think they would be causing issue as described-e.g C0 readings OK on high rate
As Landyandy suggests due to nature of subject probably best continued in CC
 
Sponsored Links
The vast majority of experienced RGI's will not give safety critical information on the open side of the forum. As your inquiry falls well outside diy territory, it is doubtful that you will find the answer here.
Admin is ususally pretty quick with verifying your registration and getting access to CC should take little time.
 