boiler in kitchen

Joined
3 Mar 2006
Messages
65
Reaction score
0
Location
London
Country
United Kingdom
hi all,is it ok to spur for boiler off the ring or should it have its own circuit?

ty bigbob :?:
 
Sponsored Links
talkin to yourself - first sign of madness.

rcd protected or not - as long as the rating of the boiler is below 3000w, then its ok on the ring circuit. assuming its a gas boiler, it shouldnt be much more than 300w.
 
Sponsored Links
bigbob said:
electrician says its ok.just want some other opinions.

Gas?
Should be OK run off the ring main. Normally supplied via a double pole switched fused spur unit.
 
If you are just installing the boiler then for convenience sake it is fine to take a fused spur off of the ring.

If you are doing a complete rewire then I would put it on a B20 MCB protected 2.5mm Radial on the Non-RCD protected side of the DB.

This will slightly lessen the loading of your ring (admittedly, not by much!) but more importantly, any future nuisance tripping of the RCD will not disable the heating.
 