Bonding Required?
T
timmyquick
Is bonding required in a bathroom if there is just one electrical item i.e the light which is outside all the zones? I have very tall ceilings (terraced house). I have a radiator in the bathroom in zone 2. There is cross bonding between the pipes Hot & Cold before plastic flex pipes to the actual taps.
12 Jan 2005
Are we talking theology or strict adherence to regulations? Bonding is required in any bathroom in a house with an electricity supply. Irrespective, I think, of whether there is electricity in the bathroom.
However, from the regulation point of view anything outside the zones is outside the bathroom, so does not need to be bonded. Just beware the light does not dangle down into a zone.
27 Aug 2003
London
No.
Regulation 601-04-01 requires that the protective
conductor terminals of each circuit supplying Class I and
Class II electrical equipment in zones 1, 2 or 3, and
extraneous-conductive-parts in these zones, are all
connected together by local supplementary equipotential
bonding conductors complying with Regulation Group
547-03.
No - you are not allowed socket outlets anywhere in a bathroom, even outside the zones.
20 Oct 2004
Does regulation 601-04-01 mean that everyone should have the earth terminal of there shower, extractor fan etc. connected to the earth on there pipes and bath etc???? And has anyone ever done because i've never seen it done after all any class 1 appliances should have an earth leading back to the main earth rail and class 2 may not in most cases have an earth terminal.
9 Jan 2005
Yes it does. And the NICEIC check for it on thier inspections. I have been coonecting the cpc in a circuit to the piping in bathrooms since the regulation was introduced. The cpc in a class 2 appliance is terminated in a connector block for the provision of the appliance ever being changed to a class 1.
27 Aug 2003
London
Yes.
Widely, I believe...
Then you've never seen it done properly..
You're right about Class IIs, but the cpc of the circuit should be connected to the bonding. And I think I see some confusion here. This is not about earthing, it is about equipotential bonding. It's done to equalise the potential of extraneous-conductive-parts, not to provide an earth for appliances!!
14 Sep 2004
when we re-wire a house we take a 4mm from the light to the rad and to the sink
20 Oct 2004
Thanks for the response guys , I served my time as a maintenance electrician in a factory (where I still work), so have never had to wire a new circuit in a bathroom but have changed light fittings in the past and never noticed a 2.5mm or 4mm bonding cable although it probably depends on the zone the light was in or if the regs where in place when the light was installed.
This leads me to another question, if I where to replace a light fitting within a bathroom Which I can do without notifying building control but it required the bonding to be upgraded (Which I can't do without notifying building control) does that work have to be done to satisfy the building regs or could a minor works cert be written and this be written in as a departure from the regs so the owner knows there is work required???
27 Aug 2003
London
What would you like the answer to be?
Seems to me that you can pick any reasonable interpretation of the various overlapping rules, and that as long as what you have done is not demonstrably unsafe, there isn't a local authority in the land that is going to try to take you to court.
Similar threads