Bringing a recessed 2G socket flush on battened plasterboard – best method?

Joined
25 Nov 2025
Messages
12
Reaction score
0
Country
United Kingdom
Hi all,

Our wall has been overboarded with plasterboard on wooden battens, which has left an existing 2G socket recessed roughly 20–25mm back from the finished plaster surface (photo attached).

10193.jpg


I'm looking for the cleanest, regulation-compliant way to bring the existing white plastic faceplate forward so it sits flush on top of the plaster, ideally without having to disconnect and re-terminate the circuit wiring if I can avoid it.

Given that there are timber battens behind the plasterboard, what is the preferred method here?

• A 2G 25mm galvanised steel extension box: Removing/drilling out the extension box's own screw lugs so long M3.5 screws pass straight through and clamp the faceplate, extension box, and rear back box tightly together (and whether a separate earth flylead is still required if it's clamped metal-to-metal like this)

• A 2G dry-lining box: Fitted into the plasterboard with the rear knockouts removed so no earthing is needed

• Extra-long M3.5 screws alone (with or without an intumescent pad/spacer)

Any advice on the neatest and safest approach would be much appreciated. Thanks!
 
First, get that socket out in front of the plasterboard and let’s see how big the hole has become.

You really should have removed the sockets first……
 
Actually, better idea. Buy new sockets. Remove the old ones and just drop them down behind the plasterboard. Now you can fit the new sockets without having to enlarge the hole.
 
I think that the hole is clearly bigger than the socket. I think it's going to need some clever plastering work, possibly using a 3d printed template, to fix that. The rough way would be one of those plates that make an accessory larger behind.
 
You don't need to rip the plasterboard apart mate. Grab a 2-gang socket extension collar/box and some 50mm or 75mm M3.5 socket screws. The collar sits inside the cutout and bridges the 20mm gap directly to the metal lugs in the original backbox so your cables aren't exposed to plaster dust or timber, and keeps it fully compliant without replacing the backbox.
 
You are very unlikely to get the socket moved forward without disconnecting the cables and to do that I suspect you will end up damaging the the new plasterboard

Who did that?
 
You don't need to rip the plasterboard apart mate. Grab a 2-gang socket extension collar/box and some 50mm or 75mm M3.5 socket screws. The collar sits inside the cutout and bridges the 20mm gap directly to the metal lugs in the original backbox so your cables aren't exposed to plaster dust or timber, and keeps it fully compliant without replacing the backbox.

I was originally thinking of grabbing an open-back 25mm metal extension box (similar to this Knightsbridge 2-gang box) and using 50mm M3.5 screws going all the way through into the original backbox.
There isn't much info online about fitting them this way would I need to earth the extender separately with a fly lead, or would the physical contact with the original backbox and the M3.5 screws be enough?
 
Is it a solid wall?

What I'm getting at is that if there isn't slack on the tails, they might struggle to reach.

You say the gap is 20-25mm. If it's 20, a 25mm box will sit proud of the finished surface.

You can get 2 gang plastic spacers that are 20mm, like this.

Screenshot_2026-11-24-13-39-17-386_com.android.chrome.jpg


If the tails are not long enough, they can be extended.

You might need to tidy up the edges of the plasterboard with Toupret (or your chosen filler).
 
• A 2G 25mm galvanised steel extension box: Removing/drilling out the extension box's own screw lugs so long M3.5 screws pass straight through and clamp the faceplate, extension box, and rear back box tightly together

Why not just screw the extender to the existing box and the socket to the extender, instead of all that faff?

1795528753722.png
 
Is it a solid wall?

What I'm getting at is that if there isn't slack on the tails, they might struggle to reach.

You say the gap is 20-25mm. If it's 20, a 25mm box will sit proud of the finished surface.

You can get 2 gang plastic spacers that are 20mm, like this.

View attachment 427348

If the tails are not long enough, they can be extended.

You might need to tidy up the edges of the plasterboard with Toupret (or your chosen filler).

Well I'm going to find out tomorrow morning been working 14hr shifts so Im hoping there is enough slack to pull it through otherwise I'll be doing what morqthana suggested
Why not just screw the extender to the existing box and the socket to the extender, instead of all that faff?

View attachment 427349
 