Now compare that to the total of your rads using Stelrad Elite Catalogue to see if they are similar.D0 shows it set to 14kW
The flow temperature is probably set to 67C. Is the temperature control on the front of the boiler set to max or something lower?d40 = 53c; d41 = 43c 10C differential
After 2 minutes: d40 =67c; d41 = 43c 24C differential
4 minutes: d40 = 67c;d41 = 45c.22C differential
At 14kW output the max flow rate should be 10 litres/min (0.6m³/hr; 0.17 litres/sec. Depending on which speed you have the pump set to, the head will vary from about 3m to 5m. This is well within the range of your ABV.
D_Hailsham
I'll do the calcs later.
The flow temperature shows on the display panel as you move the control. So yes, I probably had the control set to 67c but there is still some movement left before maximum.
Still think the ABV is a problem (unless the system really is building up too much pressure