That boiler has a internal ABV (automatic bypass valve), If it took an hour for the boiler outle to feel like 70C then something definitel wrong, its possible, if unlikely, that th ABV is faulty. The pump head at its max constant (pressure) of 400mbar, 4.0M, should give adequate circulation except the boiler HEX is partially blocked.
Assuming the boiler/rad returns at a "lukewarm" 30C, then the rads are T30 with 51.4% output of their T50 rated output.
A reality check on the actual boiler output is, when the boiler is running steadily after say a hour, take a snapshot of the actual gas meter, then exactly 3 minutes (to the second) take another meter snapshot, the gas consumption/hour is the readings difference X 20, X this by 11.0 to get the boiler input in kWh, X this by say 90% (boiler efficiency) to get the boiler output in kW.
Have or can you you range rated the boiler to a lower output?.
Assuming the boiler/rad returns at a "lukewarm" 30C, then the rads are T30 with 51.4% output of their T50 rated output.
A reality check on the actual boiler output is, when the boiler is running steadily after say a hour, take a snapshot of the actual gas meter, then exactly 3 minutes (to the second) take another meter snapshot, the gas consumption/hour is the readings difference X 20, X this by 11.0 to get the boiler input in kWh, X this by say 90% (boiler efficiency) to get the boiler output in kW.
Have or can you you range rated the boiler to a lower output?.