That's a good question, John, that I have sort of been asking myself - but in a somewhat different way. I dropped the pressure from the default 250mb in order to try to reduce noise from the lockshield on the rad nearest the boiler (it's actually very near). With the system balanced, all the rads were receiving flow and had the same mid-panel temperatures but many lockshields needed to be open just 1/4 turn or even a bit less and, even then, I struggle to get 15C, let alone 20C drop between flow and return. So yes, I have been asking myself why it is that, with the lowest pump map available, I am still needing such small lockshield openings, which are of course then rather critical, and still not achieving 20C drop. If I were to increase the pressure again, would this not just make the issue worse?
I have just been round checking rad flow and return temperatures and there are some adjustments needed but only one rad had a drop of 15C - all the others were less. I have inherited a system that has both very short and very long 15mm pipe runs that I can't do much about because the long ones are buried in floor screed and its pretty impossible to do something different. I do think I shall be able to bring things back into balance at 150mb; it's only out because of disturbing lockshields and not having reset them quite right yet.