So following having a read the other day of both the on site guide and the full BS7671 regs that I have, it dawned on me how much of a impact grouping of cables as per table 4C1 has, and how I suspect that what my electrician did back in 2013, violates the regs.
I'm trying to work out that if doing things by the big book per se, (1) if my own calculations are correct and my electrician back in 2013 violated the regs, (2) If I have made a mistake in my calculations, or (3) if there is some exception for short runs of cable, say 2 meters or so where they run up from the DB into the loft before they get disubstituted around the house, not that I can find any such exceptions in the regs.
So see image below for my exact calcs, but having 10 circuits in my house and with all circuits going through around 2 meters of 50x50mm trunking up from the DB into the loft, I can't help but feel that the regs may have been violated if doing things to the letter? Where am I going wrong, or am I??
Based on my own calcs and accounting for the omission of the two circuits that have a load <30% of their tabulated grouped rating, I work out that due the grouping of 8 cables that the my two 32A circuits should have had cable rated for 61Amps.....That's 10mm² cable if clipped direct all the way using method C (i.e. not in the 2 meters of trunking) and not accounting for other factors.
And yes, I am also aware that trunking (Method B) de-rates the 4mm² T&E feeding my kitchen sockets to 30A which is less than the 32A of the MCB.
Help me, I must surely be making a silly mistake somewhere with the grouping factor!?
Excel spreadsheet above is linked here: https://www.grottotree.com/public/Electrical-Diversity-Calcs-To-Share.xlsx
Regards: Elliott.
I'm trying to work out that if doing things by the big book per se, (1) if my own calculations are correct and my electrician back in 2013 violated the regs, (2) If I have made a mistake in my calculations, or (3) if there is some exception for short runs of cable, say 2 meters or so where they run up from the DB into the loft before they get disubstituted around the house, not that I can find any such exceptions in the regs.
So see image below for my exact calcs, but having 10 circuits in my house and with all circuits going through around 2 meters of 50x50mm trunking up from the DB into the loft, I can't help but feel that the regs may have been violated if doing things to the letter? Where am I going wrong, or am I??
Based on my own calcs and accounting for the omission of the two circuits that have a load <30% of their tabulated grouped rating, I work out that due the grouping of 8 cables that the my two 32A circuits should have had cable rated for 61Amps.....That's 10mm² cable if clipped direct all the way using method C (i.e. not in the 2 meters of trunking) and not accounting for other factors.
And yes, I am also aware that trunking (Method B) de-rates the 4mm² T&E feeding my kitchen sockets to 30A which is less than the 32A of the MCB.
Help me, I must surely be making a silly mistake somewhere with the grouping factor!?
Excel spreadsheet above is linked here: https://www.grottotree.com/public/Electrical-Diversity-Calcs-To-Share.xlsx
Regards: Elliott.