I attended a job today.
A lighting fault.
Customer said she got home during the day (no lights left on) and the fuse had blown for downstairs lights.
The board had two 5A fuses, one intact, feeding the upstairs lights and one blown. The blown one is connected to a sliced-off length of 1 milli that has been shorting.
My inital thoughts were maybe the cable had been sliced through by accident or by a rat. So I looked for the other end, but could not locate it.
This seems unlikely now, so I thought about the other option: that the downstairs and upstairs lighting are linked and the downstairs lighting has gone off because of an open circuit live or neutral.
Several things hint this may not be the case:
Usually, in a one-lighting-circuit house, the downstairs lighting is wired first. In this case, the upstairs is fully functional, so that would imply that if the circuit was wired as one, the feed from the fusebox must have gone to the upstairs first.
Usually, in a one-lighting-circuit house, the strappers are a twin & earth & the feed is connected to the hall switch with the switchwire at the landing switch.
In this case, the link from the landing switch position to the hall switch position carries 3 conductors (albeit twin and earth, not 3 core!
)
There is no continuity between the hall ceiling rose cpc and the CU earth bar.
That means all three conductors are open-circuit.
I have been round all connections on the upstairs lighting. There is nothing loose or disconnected.
The blown fuse is labelled downstairs lights.
To my addled mind, the above things make it likely (though by no means certain) that the severed cable I found is the feed to the downstairs lights.
The one thing bothering me is I cannot locate the other end of the severed cable...
Can you offer any thoughts, please?
A lighting fault.
Customer said she got home during the day (no lights left on) and the fuse had blown for downstairs lights.
The board had two 5A fuses, one intact, feeding the upstairs lights and one blown. The blown one is connected to a sliced-off length of 1 milli that has been shorting.
My inital thoughts were maybe the cable had been sliced through by accident or by a rat. So I looked for the other end, but could not locate it.
This seems unlikely now, so I thought about the other option: that the downstairs and upstairs lighting are linked and the downstairs lighting has gone off because of an open circuit live or neutral.
Several things hint this may not be the case:
Usually, in a one-lighting-circuit house, the downstairs lighting is wired first. In this case, the upstairs is fully functional, so that would imply that if the circuit was wired as one, the feed from the fusebox must have gone to the upstairs first.
Usually, in a one-lighting-circuit house, the strappers are a twin & earth & the feed is connected to the hall switch with the switchwire at the landing switch.
In this case, the link from the landing switch position to the hall switch position carries 3 conductors (albeit twin and earth, not 3 core!
There is no continuity between the hall ceiling rose cpc and the CU earth bar.
That means all three conductors are open-circuit.
I have been round all connections on the upstairs lighting. There is nothing loose or disconnected.
The blown fuse is labelled downstairs lights.
To my addled mind, the above things make it likely (though by no means certain) that the severed cable I found is the feed to the downstairs lights.
The one thing bothering me is I cannot locate the other end of the severed cable...
Can you offer any thoughts, please?