Can I have 2 consumer units?

Joined
6 Sep 2008
Messages
2,334
Reaction score
258
Country
United Kingdom
sorry for the potentially dumb question; If I need a 20 way cu, is it possible to buy two 10 ways? Is there a permitted way to split the feed? I ask because smaller CUs are available locally, 20 way are not
 
Sponsored Links
Yes.

Henley block.

Just make sure they're fire proof.

Oh wait, they're not switchgear so you don't need to bother. It's only switchgear which have poor connections and spontaneously combust all the time. Junction boxes are immune, because LFB say so.
 
Last edited:
Heh, yes.. I hope I'm not still building when Amendment 4 is issued, banning plasterboard pattress boxes and mandating galv..


LFB have a nice website you know, that has fire stats on. 21500 fires a year*, and the statistical rise that caused the concern that led to Amendment 3?
150 fires

Woo

*some of these are outdoor or vehicle
 
Henley block.
Or if you can distribute the loads suitably, you could use an MCB in the first unit as a sub-feed to the second unit. That might even save on cable runs for branch circuits if it means you can locate the second unit at some other location nearer to the loads it serves.
 
Sponsored Links
you can also get tap offs that fit the board, they look like mcbs but are straight through connecters that take 25mm cable, using one of them would keep the main switch for "one single point of isolation"
 