...spur off a ring main with a blue 16A socket?

clodhopper said:...spur off a ring main with a blue 16A socket?
bas said:Or maybe it would be OK if you used 4mm²? An interesting one
toasty said:Our comms rooms here are wired using 16amp blue commando sockets straight into CUs with 32A breakers using 4mm SWA
Spark123 said:I believe the 16A ceeform sockets are allowed to be fused up to but not exceeding 20A.


RMS said:I'm under the impression that spurring off a socket should not really exceed 13amp. ie. the rating of the socket.
clodhopper said:RMS said:I'm under the impression that spurring off a socket should not really exceed 13amp. ie. the rating of the socket.
That can't be right. The point in a circuit where a connection is made can't be relevant can it? The current flowing through the 13A socket will be 0A only the 16A socket and the ring will be taking the load.

RMS said:clodhopper said:RMS said:I'm under the impression that spurring off a socket should not really exceed 13amp. ie. the rating of the socket.
That can't be right. The point in a circuit where a connection is made can't be relevant can it? The current flowing through the 13A socket will be 0A only the 16A socket and the ring will be taking the load.
The point where you connect the load in a ring final circuit can be relevant depending on the size of the load.
If an electrical load draws a current of 13amps from the supply then the full 13amp load will be drawn through the point of load. Obviously resistance and temperature can effect the current.