Can I...

clodhopper said:
My intention is to spur off the ring at the socket with a 16A socket as this is by far the easiest solution. I cant find any reg which stops me doing this though as some of you have said, it doesnt seem right.

Theres probably something in the bit on overcurrent protection. :wink:
 
Spark123 said:
clodhopper said:
My intention is to spur off the ring at the socket with a 16A socket as this is by far the easiest solution. I cant find any reg which stops me doing this though as some of you have said, it doesnt seem right.

Theres probably something in the bit on overcurrent protection. :wink:

Don't see that. It's a 32A ring main. A 16A socket sounds to me to be lighter on potential current drawn than a double 13A socket
 
A double socket is rated at 13A total :wink: the problem with what you propose to do is you have the appliance flex unprotected except by the 32A RFC breaker... I'd spur to your 16A ceeform via a 16A breaker :)
 
Adam_151 said:
A double socket is rated at 13A total :wink: the problem with what you propose to do is you have the appliance flex unprotected except by the 32A RFC breaker... I'd spur to your 16A ceeform via a 16A breaker :)

Right. Now I understand. Cheers
 