What is this pump and what does it do .
circulates the water.
And what is the best number to have it on .
lowest that will work
2nd my heat does not seem to turn down .
this is controlled by the thermostatic radiator valve (TRV) and lock shield valve in the main.
Should the valves on the radiators be fully open .
No.
So the system is, the pump circulates the water either through the radiators if the TRV is open, and the by-pass valve if all TRV's are closed, and the boiler monitors the return temperature and adjusts output, so the return water is cool enough to gain the latent heat from the flue gases.
This system has a flaw, the boiler would never switch fully off, it would cycle off/on all the time, so we try to include a method to turn it fully off, the traditional method was to put a wall thermostat in a downstairs room, with no alternative heating, and normally kept cool, and no outside doors, there is often no such room. So there are other methods, like the TRV linked to a hub, and the hub turns the boiler on/off, or up/down if that type of thermostat.
The boiler often does more than heat one set of rooms, either zones of rooms, or room and domestic hot water (DHW) and to do this we have zone valves, inside the zone valves there is often a micro switch and if that switch sticks closed, then the boiler will not stop running.
I have this one . But it's near the front door . Probably the coldest part of the house . Is this why the radiators are so hot . Because this is cold .
As a check - turn that thermostat down to minimum, less than 10 then check you radiators, after an hour. They should all be completely cold.
The lockshield valve. Should I have this fully open mate . Sorry to be a pain . I'm a joiner and this is all new to me .
Cheers mate
Had same problem with mother's house, long large radiator along the wall, then a doorway, then the thermostat then another door. Theory is great, but to get circulation with a staircase opposite the radiator is simply not going to happen. So close the lock shield valve, so rest of house can heat up, and open door, and hall freezing cold, open up the lock shield valve, so hall is warm, and rest of house is cold.
Only method seemed to be to fit a thermostatic radiator valve (TRV) the mechanical TRV has a massive droop, (difference between on and off temperatures) and it is analogue, so set at say halfway between 2 and 3, it would start to close at 17°C and not fully close until 20°C so a wall thermostat set at 19°C would switch off in fullness of time, but it would take long enough so rest of house warm first, but from 6°C after door opened to 17°C recovery was fast. This was OK with a simple warm thermostat.
But I moved to a programmable thermostat, so now for it to work, the TRV also needed to be programmable, this is more of a problem, as the droop on an electronic TRV head is more like 1°C not 3°C, so it becomes harder to set up. So start to look at linked TRV heads, the Drayton Wiser system will auto combine the wall thermostat and TRV head if both assigned the same room name, and the Kasa TRV head can have remote sensors to control it.
The main problem, is the installers, don't live in the homes they install the systems into, except their own home, and users often have no idea of the options available. To get someone to say, I have use Tado, Tapo (Kasa), Evohome, Wiser, Hive etc. And you set it up like this, seems to be rare, we get the "we do it this way, because we have always done it this way." brigade, who are still living in the 80's before we had condensing boilers, I have also worked with the old one pipe system, steam goes in one end, water drips out the other, but only because a work on a heritage railway, where boilers still boil water, today if a boiler boils water we consider it faulty.
So in my house I have eQ-3, Energenie, Kasa, and Wiser TRV heads, I got it wrong to start with, was told Energenie worked with Nest, it does no work any more, when I got them eQ-3 were cheap, (£15 each) and I used Kasa as already using Tapo, both are TP-Link so use the same hubs, but Wiser transformed my system, it works, so once I got it working, did not need to try anything else.
Having a wireless thermostat that you can take room to room, or move around the room, to test where is the best place, is a huge advantage, until the cat sleeps on it and one is left scratching one's head why is the room so cold.
But my first two homes worked well, both open plan, so a single thermostat was enough, mother's house and this house had the thermostat in the hall, silly single place really, but one has to look at 1970's houses to understand why, the central heating was to get the home warm in the morning, before going to work, or evening having just got back, but main heating was still the open fire in the living room, at that time we wanted the living flame, central heating back then was only to warm house while one laid and lit the fire, so a thermostat in the living room would not work, as the fire would stop central heating working in any other rooms.
But today is all about each room being its own zone, with a thermostat in every room, OK that thermostat may be a TRV, but the whole concept has moved on.
You keep saying that but not everyone agrees.
Yes, you make a good point, people want to cut corners, and will read laws and regulations to suit what they want to do, rather than what they know jolly well what they were meant to require, seems, so many people need to return to school and learn to read.
The bi-colour combination green-and-yellow shall be used exclusively for identification of a protective conductor, and this combination shall not be used for any other purpose.
(Note the full stop)
Single-core cables that are coloured green-and-yellow throughout their length shall only be used as a protective conductor and shall not be over-marked at their terminations, except as permitted by Regulation 514.4.3.
(some it seems thought this meant that if not single-core then could be over-marked).
The same with having just two RCDs in a consumer unit, and latter the regulations clarified what was meant, which is a problem for those who chose to misread the regulations.
We all know the TRV can be used to give us numerous zones, each one can be controlled independently, and we also know people chose not to use the function. I have 14 electronic TRV heads, and I have chosen to only link one to the hub, so only one can turn on the boiler, that was my choose, I considered a £15 eQ-3 head which is not linked, but still programmable was enough for the other rooms.
Now the Energenie head is a different story, I read it would work with Nest, and I expected them to work with Nest in the same way as the Wiser ones work, I was conned, they don't work with Nest since Google took them over. And even before that they worked the wrong way around. The Nest told the TRV what to do, rather than the TRV telling Nest what to do.
I also made a mistake with Kasa, this was my error for not checking there was a wireless option, think there is now? But I am an electrician not a heating engineer, to me engineer means trained better than level 3, so at least Fdeng behind their name.
There are no regulations that require each room to be zoned.
Our rads are old. Very old, so i keep the valve open at max on those in the liv. room and bedroom, then others in rooms less used at a high enough mark to avoid them rattling when our more modern combi-boiler tries to push out extra energy if the weather demands a higher temp. Fortunately, this winter has been v. mild; mild enough to not require setting the thermostat on max (22) and maintaining a steady 21 degrees for most of the day. As a result, the monthly DD came down by £30.(y) Having the loft re-insulated a few years ago with thicker layers certainly helped keep heat in the house rather than losing it through the roof and i swear the Wallrock lining paper i've used in bedrooms has made a difference.
@denso13 I have been told so many times things like
UK Building Regulations (Part L) mandate boiler interlocks, requiring heating systems to have independent time and temperature controls (like TRVs, thermostats, programmers) and a boiler interlock to prevent simultaneous heating/hot water demand, ensuring efficiency by only running the boiler when needed and reducing energy waste, especially with recent 2022 updates enforcing zone control and higher efficiency standards.
I have not read exactly what it says, only the official guidance, so maybe I have got that wrong.
@Odds I also have an old system C Plan, with oil boiler, the biggest change was when I started using an immersion heater, that really dropped the bill for oil, I had not realised how inefficient the oil boiler was at heating DHW, still heat it in winter, but not the summer any more. But the TRV heads closing when room hot enough, has also really dropped my oil bill as well.
Just pointing out that zoning every room isn't a requirement.
I am of the view that a properly designed system doesn't need individual zone controls for every room, and that it can sometimes do more harm than good.
Now, there may be some that aren't designed properly and benefit from them in some way, but that is a long way from saying that every property should have them.
Last time I checked, several years ago, I decided that, the fitting of basic TRV's, a room thermostat, and some sort of timer, plus different boiler output temperature options for CH v HW, fully satisfied the requirement.
Dittto, interesting to note that you have different boiler output options for CH and HW
Yes, I will be the first to admit, I have looked a few times at the zoning of the home, and the control of the boiler by the zones, and it is not as simple as it first looks.
I had to start with thought linked TRV heads were the bees knees, but after fitting one in wife's bedroom, realised not as straight forward as I first thought, with non-linked, if I set my bedroom at 20°C, radiator will not heat up unless the boiler is running, so can set it a bit on the high side, and it does not matter.
But do same with wife's room, and it will fire the boiler, and to have a whole boiler run to heat one room is a bit silly, so I want rooms upstairs to have some heat, but want them all to heat at the same time, with one boiler firing, so set her room to say 17°C but my room at 18°C so if boiler fires heating two rooms.
So I am left with working out when each TRV with change temperature so rooms can all be heated at the same time, so I end up with 1768484525226.pngin this case the kitchen, but it does not ever reach the temperatures set, the more expensive TRV heads give a graph Kasa living room.jpgWiser living room and bed room 30-31.jpgand I am sure if I studied it more, I could improve when the heating turns up/down, to better suit what I want, yesterday 1768485001390.pngthis seems to show the room better following the settings since new double glazing has been fitted, but I only look at the graphs when writing on forums, I can't really work out how it helps.
With the original Energenie heads in mothers old house, the modulating boiler kept the temperature spot on, but with an on/off oil boiler we get a fair hysteresis as boiler fires and cools, 1768485528405.png so the heads don't work nearly as well as when used with the gas boiler. I look 1768485877528.png and it says heating running, but can't hear the boiler, the displays look good
but the Nest Gen 3 in hall does very little more to the old cheap one in the last house ae235.jpgand since the heating worked in last house, never really looked at it. It was only when we moved first to mother's house and then this one, in both cases the heating was not good enough, that we looked on how to improve it, had it worked, then I would have never looked. The problem with this house was having the main thermostat in the hall, and the hall cools too slowly, you can adjust heat up time with the lock shield valve, but you can't adjust cool down time.
I swapped the old heat only boiler, for a new one, and took the opportunity to do a general upgrade, at the same time. The old one, ran on a preset temperature, feeding a 3-port, able to heat CH, or HW, or even both simultaneously. Latest one, only does one at a time, using different output temperatures. For CH, the controller, decides just how hot it needs to be, to match the demand. For HW, it runs at 70, to get the cylinder to 60.
The cooler the boiler is able to run, the more economical it is.