What is the amp value of the MCB that is tripping? Is it an MCB or an RCBO (an RCBO will have a test button on it).
both 63amp rcbo trip
Any chance of a bit of consistency and accuracy?its a 32b mcb thats tripping
They aren't RCBOs they are RCDs.before that there is the 100amp main switch and a 63amp rcbo
Taylortwocities";p="2429034 said:What is the amp value of the MCB that is tripping? Is it an MCB or an RCBO (an RCBO will have a test button on it).
ive just tested it and its the 63amp with a test button on it that trips sorry my mistake and the 32b that stays on sorry for the confusion
I'm out.the connection box under the hob is well labelled live neutral earth so i know i have'nt made a mistake there i didnt need or touched any other connections/wires everything is ok when i switch the wall switch on then when i turn a hob ring on a red light flashes for a millisecond then it trips the mcb should i just call the sparky back if so what is and how dangerous is an unprotected circuit just the word "unprotected" worries me