Haha, just looked at the boiler innards. Seems to have an inbuilt pump!
That'll teach me, it should teach Alex too but I doubt that it will.
So it does. Have you noticed it's a big one and not a 15/50 or 15/60? I'd say it's a 26/65...
The standard Grundfos domestic 15-60 gives a maximum of 1.1 litres/s
The law says that it should be fitted to manufacturers instructions. The manufacturers instructions require that it is fitted by someone with commercial training.It is 46 kilowatts. A domestic man can fit it. The law.
Wrong. the dividing line is 70 kilowatt. Makers cannot overrule the law on classification.
It is 46 kilowatts. A domestic man can fit it. The law.[/b]
Lo and behold it does have a pump! The know it alls were saying it needs an expensive one that you have to buy. But to get the minimum follow through it a domestic speed is all you need. No doubt this pump can pump greater flows, but that is not required for this 5 bed house.Haha, just looked at the boiler innards. Seems to have an inbuilt pump!
The makers gave the figures.The standard Grundfos domestic 15-60 gives a maximum of 1.1 litres/s
Not once you factor in the pressure drop across the hex it doesn't. But there's no point trying to reason with the fanatical.
I have wiped the floor with this Dan fellow, which is not difficult,
Have to say I've just sat down with some popcorn for this as well!
Dan I hope you are suitably chastised?
I am tying to find a link for an extra long handled shovel for this guy as he is digging just the deepest hole for himself.![]()
Dan really was. He wrote he had the makers instructions and said an external very big pump was needed when one was inside. Fun it was.I have wiped the floor with this Dan fellow, which is not difficult,
If you are GS registered you should have seen the bulletin/leaflet.
Commercial gas criteria has changed. The old kW, pipe and meter size requirements are no longer in force. Changes include.
* The allowance of 35mm pipe from a U6 meter for domestic up to a carcass volume limit.
* The allowance of domestic ticket work on up to a U16 meter with up to 35mm pipe on a limited carcass gas volume.
* The installation of multiple boilers up to carcass volume limit as long as total output doesn't exceed 70kW limit.
* THE CLASSIFICATION THAT ANY BOILER LISTED IN MANUFACTURERS COMMERCIAL RANGE IS A COMMERCIAL BOILER AND CAN'T BE LEGALLY INSTALLED WITH DOMESTIC TICKET, whatever the output, whatever the meter/pipe arrangement.
It's regulations that have made this change, not the manufacturers.
Enough to go around a loop in low loss header. The boiler has its own pump has your instructions would have told you.Hhmmm.... I wonder how much pump head is left after the HEX ?.
You are getting there, and the boiler can run at about 12 kilowatt.Also to most others that a house only needs its rated heat loss of say 10-18 kW when the temperature is -1 C or below outside.