- Joined
- 17 Aug 2010
- Messages
- 2,749
- Reaction score
- 455
- Country
Exactly.
As I think we've all agreed, that is probably sensible - but that's rather different from being (legally) 'required'.Re the landlord bit, many letting agents won't take a property on without a recent (< 5 years) EICR- the agents i use justified it as an electrical MOT, evidence of being a responsible landlord and useful if the tenants bodged something in which later caused damage/injury.
Dismantling is strongly discouraged during periodic inspection and testing for precisely that reason.As I think we've all agreed, that is probably sensible - but that's rather different from being (legally) 'required'.
'Something bodged in' by tenants is certainly an important issue although I would imagine that such would usually (albeit not always) be apparent without doing a 'full EICR' - or, at least, there would be enough in the way of 'suspicious signs' to indicate that a full EICR was advisable..
There's one aspect of EICRs which rarely gets discussed. Inspection, of any degree of extent or detail, is always fine (and harmless) but 'testing' is a somewhat different matter if it involves (as 'full testing' will) removing and re-installing conductors in some terminals - so I wonder how many problems have arisen as a result of loose/faulty connections caused by an EICR being undertaken ... and if that does happen sometimes, the more EICRs are done on an installation, the greater the risk. It was probably rather OTT, but I was 'brought up' with the notion that one should not repeat a screwed connection onto the same part of a conductor more than three times!
Kind Regards, John
That would clearly be desirable, if it were possible, but I wonder to what extent that is how things work in practice?Dismantling is strongly discouraged during periodic inspection and testing for precisely that reason.
To a very large extent. Minimum dismantling should always be exercised.That would clearly be desirable, if it were possible, but I wonder to what extent that is how things work in practice?
Kind Regards, John
Again, we are totally agreed that minimal (ideally no) dismantling is desirable. However, I'm still not sure how close to that ideal most people get. I would have said that some tests cannot really be done (at least, not directly) without some dismantling.To a very large extent. Minimum dismantling should always be exercised.
I'm not sure that they would issue a completion certificate for work carried out over four years ago, even if they had a recent EICR, would they? If the work wasn't notified at the time (as it should have been) one could go through a 'regularisation' process, but I think that's even more expensive than notification.So if the buyer wanted a certificate that badly then the LABC would need paying their fee, and they would send some one to do an EICR and would issue a completion certificate ...
What testing appropriate to periodic inspection and testing do you feel requires dismantling?Again, we are totally agreed that minimal (ideally no) dismantling is desirable. However, I'm still not sure how close to that ideal most people get. I would have said that some tests cannot really be done (at least, not directly) without some dismantling.
Kind Regards, John
It was really intended more as a question than I statement ("I would have thought that...") but I would have thought that (again ) the most obvious example would probably be 'ring circuit continuity' (which might sometimes be required as part of an EICR)?What testing appropriate to periodic inspection and testing do you feel requires dismantling?
If one was to follow the guide lines, then one would remove a sample of sockets and switches and ceiling roses to check for grommets and sleeving, as to if this really helps not sure, the fault with daughters house was a screw had touched the neutral wire where poor stripping of cable had exposed copper, your unlikely to find this fault by removing socket fronts, in fact more likely to cause a fault.What testing appropriate to periodic inspection and testing do you feel requires dismantling?
Yes I agree that ring final circuit continuity will require it, but generally just simple end-to-end testing and usually carried out at a socket-outlet.It was really intended more as a question than I statement ("I would have thought that...") but I would have thought that (again ) the most obvious example would probably be 'ring circuit continuity' (which might sometimes be required as part of an EICR)?
Kind Regards, John
By definition, one could not undertake any 'end-to-end' measurements on an intact ring circuit (which has no 'ends' ) - so, no matter where you do the 'dismantling', you'd have to do some!Yes I agree that ring final circuit continuity will require it, but generally just simple end-to-end testing and usually carried out at a socket-outlet.
'Said' by whom??It has been said no hatch into loft does not excuse not inspecting wiring in the loft...
