Consumer Unit... too many Amps

Discussion in 'Electrics UK' started by flibberflops, 23 Dec 2020.

  1. flibberflops

    flibberflops

    Joined:
    18 Feb 2007
    Messages:
    17
    Thanks Received:
    0
    Location:
    Birmingham
    Country:
    United Kingdom
    Hi,
    I am having a new kitchen built and I assumed that I could just add an electric over + Induction hob without issue (it was previously Gas). However, as per the diagram below I have just realised that I am scuppered by a 32amp solar panel feed that is leaving me short on spare amps on the one RCCD side. I was intending to get a sparky in to just add the hob and oven wiring but i've just realised its probably going to be more involved than that. Can anyone recommend the easiest way to juggle what I have or tell me what is needed to do this properly? I haven't actually brought the hob/oven yet so I can tweak this if it makes things easier (but herindoors 100% wants to move away from gas)

    consume.jpg
     
  2. Sponsored Links
  3. Robin0577

    Robin0577

    Joined:
    16 Aug 2011
    Messages:
    548
    Thanks Received:
    103
    Location:
    London
    Country:
    United Kingdom
    Not a problem...

    1. You can apply diversity. https://www.tlc-direct.co.uk/Book/6.2.3.htm

    2, Your solar installation is an input, not a load. When generating at full capacity it might count as anything up to MINUS 32 amps in your calculations, depending on the external conditions. When it's dark outside, it will use a tiny amount of power to keep the electronics going but effectively counts as zero.
     
    • Thanks Thanks x 1
  4. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    17,121
    Thanks Received:
    1,564
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    My own 60 amp DNO fuse at 16 x RCBO's no problem. Where you may have a problem is the 80 amp RCD with 100 amp over load protection, we all know it will never reach 100 amp, and in real terms not a problem, but it depends on the electrician and how pedantic he is.

    My induction cooker has a total load if all switched on and nothing cycling as up to heat of around 48 amp but it has never tripped the 32 amp supply.
     
    • Thanks Thanks x 1
  5. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    24,285
    Thanks Received:
    2,372
    Location:
    Bedfordshire
    Country:
    United Kingdom
    Also put one light circuit of each of the two RCCBs. Then if ( when ) an RCCD trips you will still have some lights in the house
     
    • Like Like x 2
    • Thanks Thanks x 1
  6. sparxxxx

    sparxxxx

    Joined:
    8 Dec 2020
    Messages:
    197
    Thanks Received:
    20
    Country:
    United Kingdom
    How do you know your main fuse is 100Amp? The 100Amp marking on the cut out just denotes cutout size. They are usually 60Amps, which is still more than adequate for your place
     
  7. flibberflops

    flibberflops

    Joined:
    18 Feb 2007
    Messages:
    17
    Thanks Received:
    0
    Location:
    Birmingham
    Country:
    United Kingdom
    Someone has actually put a proper sticker on it saying so!
     

    Attached Files:

    • fuse.jpg
      fuse.jpg
      File size:
      159.7 KB
      Views:
      148
    • Like Like x 1
  8. sparxxxx

    sparxxxx

    Joined:
    8 Dec 2020
    Messages:
    197
    Thanks Received:
    20
    Country:
    United Kingdom
    Oh dear!!!!!
     
  9. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    17,121
    Thanks Received:
    1,564
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    Yes looked at that with my consumer unit before changed, idea is if you do some thing to trip the RCD your not plunged into darkness as well, so for example down stairs sockets and up stairs lights together on one RCD and then upstairs sockets and down stairs lights on the other.

    However splitting sockets side to side has many advantages to up/down, more even load, more even length, no need for emergency cables up/down stairs, so my house was split side to side for sockets, and up/down for lights, so it was simply not possible to arrange the circuits so tripping the socket RCD would not plunge one into darkness in all rooms.

    The regulations say
    It seems many do not consider the RCD as splitting the house into circuits, it is a grey area, with the old 100 mA type S RCD they did not tend to trip very often, so no one really worried, but with 30 mA RCD's they do seem to trip far more often for what is seems no good reason.

    We are told the leakage in normal use for all circuits on a RCD should be no more that a 1/3 of it's rating, so 9 mA, but my clamp-on will only read down to 100 mA so I have no way to test, although the insulation test may show less than 1 mA, that is DC and we use AC, so we have inductive and capacitive linking which can mean quite a few mA is leaked.

    So when I did this house I used all RCBO's so if even spread across circuits I could have 100 mA leaking without tripping the RCBO's but it cost more to install.

    However if the RCD does not trip, then no problem, what I am not sure about with any item using a switched mode power supply is if there is a fault causing DC will we actually know? I consider with 14 RCBO's the risk they will be frozen by DC when required is low, so cancelled my order for type A, even with no RCD protection I would not say this house with a TN-C-S supply is potentially dangerous, to me the RCD is an extra protection, so not working is no real problem.

    The point is not if perfect, but is it good enough, and I would not really be worried if my house was like yours unless if keeps tripping.
     
  10. Sponsored Links
  11. Colin Brenton

    Colin Brenton

    Joined:
    1 Mar 2008
    Messages:
    143
    Thanks Received:
    25
    Country:
    United Kingdom
    I think 'all RCBO' is preferable to 'dual RCD', I wonder if it might become required in the next edition of the regs??

    Just a moot question, but presumably it's possible to mix type A and type AC RCBOs so each circuit has appropriate protection, without one type effecting the other?
     
  12. Astra99

    Astra99

    Joined:
    1 Feb 2011
    Messages:
    867
    Thanks Received:
    141
    Location:
    Gloucestershire
    Country:
    United Kingdom
    With both lighting circuits on the same RCD, I wonder if this is an older property, and the landing light is on the downstairs circuit's phase conductor with the neutral on the upstairs circuit! Very common setup in the days before RCDs.
     
    • Like Like x 1
  13. danechip

    danechip

    Joined:
    15 Sep 2010
    Messages:
    555
    Thanks Received:
    50
    Location:
    Kettering, Northamptonshire
    Country:
    United Kingdom
    It also has the makers black sticker on the side too. Must be wrong :(
     
  14. sparxxxx

    sparxxxx

    Joined:
    8 Dec 2020
    Messages:
    197
    Thanks Received:
    20
    Country:
    United Kingdom
    The photo was posted after my comment
     
  15. flibberflops

    flibberflops

    Joined:
    18 Feb 2007
    Messages:
    17
    Thanks Received:
    0
    Location:
    Birmingham
    Country:
    United Kingdom
    Its a Dormer Bungalow, so there is only two lights upstairs. The downstairs circuits are split 50/50
     
  16. Lectrician

    Lectrician

    Joined:
    18 Jul 2004
    Messages:
    8,466
    Thanks Received:
    397
    Location:
    Devon
    Country:
    United Kingdom
    The solar panels should not be sharing an RCD with other circuits.
     
  17. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    68,677
    Thanks Received:
    3,811
    Location:
    Crossgates
    Country:
    Cook Islands
    Perhaps so, but, Why?
     