When you say two lamps, two switches, two way, do you mean two lamps coming on together, switched from two different positions?
Conventional to me means 3 plate. But there are two other common methods:
JB (which is similar to 3 plate except all the connections usually made in the rose are made in a JB, with a single cable then feeding to the luminaire.
But more commonly is the method where the live loop is taken to the switch.
I like the 3 plate method, because you have the live loop easily accessible in the ceiling, whereas with the others, it is not.
If you want a neutral at the switch position, that is easily done when wiring the circuit.
But if you want to wire it in singles, it would be a conduit job, and this is very different.
From the supply would come a live neutral & cpc. The live drops at the first switch to the common. The neutral & cpc go to the first luminaire, and loop to the second one, along with a switched live.
Then a switched live drops from the second luminaire to the common of the second switch. Link the two switches with two strappers and you're done.
But I really shouldn't have to do your homework, should I?