most older cooker outlets run (or should) run at least 30 amps so there shouldn't be a problem converting this to a standard double outlet.
but i would replace both the cable and the fuse/MCB at the consumer unit for safety's sake. the cable because you don't know how old it is or the condition it is in where it is hidden and ideally you want a single run from consumer unit to switch (no joints) and the breaker device because you shouldn't want anything stronger than a 20 amp unit to cover a normal outlet in any case.
most older cooker outlets run (or should) run at least 30 amps so there shouldn't be a problem converting this to a standard double outlet.
but i would replace both the cable and the fuse/MCB at the consumer unit for safety's sake. the cable because you don't know how old it is or the condition it is in where it is hidden and ideally you want a single run from consumer unit to switch (no joints) and the breaker device because you shouldn't want anything stronger than a 20 amp unit to cover a normal outlet in any case.
Why not? - we use 32A mcb`s on a ring final circuit.
using 32 amp or even 40 amp MCB's to protect a ring main is commonplace but only from the consumer unit to the first junction point-thereafter 26 amp ring main cable should be used but if something goes wrong with the intermediate cable in a single installation (from consumer unit to outlet) such as it gets damaged or whatever you want to be sure the MCB is going to trip rather than supply current up to 32 amps or whatever to the damaged cable-this creates a fire hazard if the cable is rated at 30 amps it should be covered with a 20 amp MCB anyway-the maximum carrying capacity of any cable should always exceed the breaker unit that supplies it.
as you say-there is nothing wrong (technically) with using 32 amps to cover an outlet and so long as nothing goes wrong with the wiring then all should be well but safety comes first-and besides what are you going to plug into a standard outlet that consumes that amount of current?
most older cooker outlets run (or should) run at least 30 amps so there shouldn't be a problem converting this to a standard double outlet.
but i would replace both the cable and the fuse/MCB at the consumer unit for safety's sake. the cable because you don't know how old it is or the condition it is in where it is hidden and ideally you want a single run from consumer unit to switch (no joints) and the breaker device because you shouldn't want anything stronger than a 20 amp unit to cover a normal outlet in any case.
Why not? - we use 32A mcb`s on a ring final circuit.
using 32 amp or even 40 amp MCB's to protect a ring main is commonplace but only from the consumer unit to the first junction point-thereafter 26 amp ring main cable should be used but if something goes wrong with the intermediate cable in a single installation (from consumer unit to outlet) such as it gets damaged or whatever you want to be sure the MCB is going to trip rather than supply current up to 32 amps or whatever to the damaged cable-this creates a fire hazard if the cable is rated at 30 amps it should be covered with a 20 amp MCB anyway-the maximum carrying capacity of any cable should always exceed the breaker unit that supplies it.
as you say-there is nothing wrong (technically) with using 32 amps to cover an outlet and so long as nothing goes wrong with the wiring then all should be well but safety comes first-and besides what are you going to plug into a standard outlet that consumes that amount of current?
I've built a new kitchen and the old kitchen still has a cooker socket on one of the walls. Is it ok to move it to skirting level and just put a double socket there or not? It has 6mm cable.
professional";p="1038739 said:most older cooker outlets run (or should) run at least 30 amps so there shouldn't be a problem converting this to a standard double outlet.
but i would replace both the cable and the fuse/MCB at the consumer unit for safety's sake. the cable because you don't know how old it is or the condition it is in where it is hidden and ideally you want a single run from consumer unit to switch (no joints) and the breaker device because you shouldn't want anything stronger than a 20 amp unit to cover a normal outlet in any case.
Why not? - we use 32A mcb`s on a ring final circuit.
using 32 amp or even 40 amp MCB's to protect a ring main is commonplace but only from the consumer unit to the first junction point-thereafter 26 amp ring main cable should be used but if something goes wrong with the intermediate cable in a single installation (from consumer unit to outlet) such as it gets damaged or whatever you want to be sure the MCB is going to trip rather than supply current up to 32 amps or whatever to the damaged cable-this creates a fire hazard if the cable is rated at 30 amps it should be covered with a 20 amp MCB anyway-the maximum carrying capacity of any cable should always exceed the breaker unit that supplies it.
as you say-there is nothing wrong (technically) with using 32 amps to cover an outlet and so long as nothing goes wrong with the wiring then all should be well but safety comes first-and besides what are you going to plug into a standard outlet that consumes that amount of current?
If you are a spark, I pity your customers. I suggest you enroll on an electrical design course PDQ because I think that you need it.[/quot
well i have yet to recieve a complaint (or call-back) in 25 years-but then who am i to argue with the experts!
rule no1-the circuit breaker must never be the same as or exceed the specified maximum load of the supply cable-first thing i was taught in domestic electrical installation that was-i would have thought you would have known that stargazer?
you have just advised this person that he can convert to a standard outlet-without enquiring or inspecting the condition of the wiring (i doubt it has gone through a full continuity and earth leakage examination isthe cable rubber or PVC coated?-are the core wires red and black or blue and brown?)-he did say it was an old kitchen-it may not even be the correct cable!!-obviously i could not inspect the wiring myself which is why i said replace it-something any electrician worth his salt would have done.
it's not my customers that should be pitied!.
Stuff
is this a wind upmost older cooker outlets run (or should) run at least 30 amps so there shouldn't be a problem converting this to a standard double outlet.
but i would replace both the cable and the fuse/MCB at the consumer unit for safety's sake. the cable because you don't know how old it is or the condition it is in where it is hidden and ideally you want a single run from consumer unit to switch (no joints) and the breaker device because you shouldn't want anything stronger than a 20 amp unit to cover a normal outlet in any case.
in theory yes you would have to test the cable ir test ectI've built a new kitchen and the old kitchen still has a cooker socket on one of the walls. Is it ok to move it to skirting level and just put a double socket there or not? It has 6mm cable.