Cooker Cable slightly damaged . Advice on repair.

Discussion in 'Electrics UK' started by ruddyr1, 8 Jul 2014.

  1. ruddyr1

    ruddyr1

    Joined:
    21 Nov 2005
    Messages:
    57
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    Who ever fitted the kitchen in my house, which was a new build, almost screwed through the cooker circuit cable when mounting the wall cupboards.

    Ive just chased them back to fit a new kitchen and found that the cupboard mounting screw has passed through the grey outer coating and bruised the black cable inside.

    Any suggestion on how to make safe. There has never been an issue with the circuit tripping and Ive lived here from when it was first built.

    Cheers
     
  2. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    28,468
    Thanks Received:
    3,057
    Location:
    Retired to:
    Country:
    Portugal
  3. ruddyr1

    ruddyr1

    Joined:
    21 Nov 2005
    Messages:
    57
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    thing is you can see a little bit of copper, very small but still visible
     
  4. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,787
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    So not just "bruised" then.

    As you're exposing the cable anyway, might as well replace it.


    Was that because they were hard of thinking, or because the cable shouldn't be were it is?
     
  5. Belboz

    Belboz

    Joined:
    17 May 2008
    Messages:
    1,610
    Thanks Received:
    147
    Location:
    GUE
    Country:
    United Kingdom
    Silly question but why is the cooker cable behind the wall-mounted cupboards??

    I would have thought that the cables would come UP to the cooker switch from below and that the switch is situated below the wall cabinets...

    Or am I just being thick (BAS will tell me if I am...)

    B
     
  6. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    4,065
    Thanks Received:
    365
    Location:
    Herefordshire
    Country:
    United Kingdom
    When the ground floor is concrete Cables can but run under the upstairs floor and down to the cooker switch.

    If it were me I would put some silicon sealant on it.
     
  7. Belboz

    Belboz

    Joined:
    17 May 2008
    Messages:
    1,610
    Thanks Received:
    147
    Location:
    GUE
    Country:
    United Kingdom
    Thanks Andy.

    It obviously WAS me being thick....

    Albeit my ground floor is all concrete and the cables come UP...

    :oops:
     
  8. ruddyr1

    ruddyr1

    Joined:
    21 Nov 2005
    Messages:
    57
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    the ground floor is a suspended wooden floor over concrete base. the cables run from garage up into ceiling then to all the rooms and down the walls.

    The cooker cable runs down behind the plaster board wall behind the wall units to the cooker switch which is mounted between the work surface and the wall units.

    Ive cut away some of the grey insulation to examine the cable and 6mm of copper has been exposed of the black cable, non of red cable.

    To replace it I would have to add a junction box above the new units, Could I put a sleeve over the black cable then insulate the whole section?
     
  9. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    41,036
    Thanks Received:
    2,543
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    How would you put a sleeve over the black-insulated conductor?

    Kind Regards, John
     
  10. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    28,468
    Thanks Received:
    3,057
    Location:
    Retired to:
    Country:
    Portugal
    IF none of the strands of copper is damaged, you could wrap the exposed conductor with self-amalgamating tape and then wrap the whole cable.

    I wouldn't want to cut the wire unless absolutely necessary.
     
  11. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    18,403
    Thanks Received:
    1,823
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Insulation test first.
    If it passes test then SA tape etc as above.
     
  12. securespark

    securespark

    Joined:
    11 Jan 2004
    Messages:
    32,874
    Thanks Received:
    962
    Country:
    United Kingdom
    From what you have described, my bet is the IR test will pass with flying colours, but test it anyhow to be on the safe side.

    Is the cable in a safe zone?
     
  13. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    41,036
    Thanks Received:
    2,543
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Whilst I'm not disagreeing at all with what TTC and yourself have said, I wonder whether the OP does not require some more realistic/practical advice - it seems very unlikely that anyone who comes here to ask how to deal with a damaged cable will be equipped to undertake an IR test (it's so far only been described as 'IR', so he may well not even know what it means!).

    If it is felt that an IR test should be undertaken (although, as you say, I think the result is almost certain), maybe the OP should be advised to get an electrician in to undertake the test (and, whilst (s)he is there, probably deal with the cable in some way as well)?

    Kind Regards, John
     
    • Thanks Thanks x 1
  14. ruddyr1

    ruddyr1

    Joined:
    21 Nov 2005
    Messages:
    57
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    I will tape as described and then before I fit the kitchen units I will have the electrician test everything. Then if anything is wrong there is access still to the taped cable.

    The circuit has been used for the past 20 years without issue and there is no signs of scorching or soot or burning at the location.

    Even if it is ok I may just leave the section protected (as in covered) by a junction box and accessible at the rear of the wall cupboard. Ie not plastered over.

    cheers
     
  15. dhutch

    dhutch

    Joined:
    12 Oct 2011
    Messages:
    1,651
    Thanks Received:
    101
    Location:
    Wirral
    Country:
    United Kingdom
    [quote"]bruise (bruːz/) noun
    an injury appearing as an area of discoloured skin on the body, caused by a blow or impact rupturing underlying blood vessels.[/quote]

    I don't think cables bruise!

    - If its only damaged the covering, there might be repair options.
    - If its damaged the copper, small nick, dent, etc, a join/replacement is needed imo.



    Daniel
     