Cooker circuit.

  • Thread starter Thread starter DP
  • Start date Start date
Holms...

It says in the regs that you can use a contactor manufactured to a particular standard for isolation. What is it about this that you cannot accept?

You're so hung-up about what they do & what they're called...YOU can ring the IET.

They're open between 10 & 12 and again between 2 & 4.

But the IET won't necessarily know their correct name.

You would need to contact the manufacturer...as I've stated before.

Good luck getting through, they're usually quite busy.
 
So BAS and secure spark, even with your knowledge of the 17th edition neither of you can tell me anything about these isolating contactors. I only want to know the correct name and what they're called.
They are called contactors.

If they comply with BS EN 60947-4-1 then they may be used for Isolation, Emergency Switching and Functional Switching. For isolation they have to bear an IEC isolation symbol, but you don't don't need to know the details of that.

I imagine that there are a number of makes available.
 
To avoid digression in another topic, I'm shifting this reply to where it belongs.

Also I've learnt all about contactors used as isolators - and I know that no-one involved that debate new anything about them - and whats more to the point - they still don't. :lol: :lol: :lol:
What makes you think I knew nothing about contactors and still don't?

Also I'm sure that DP, RF Lighting, Click-Sure, Spark123, Calder & securespark would like to hear your justification for saying that they knew nothing about contactors, and still don't.
 
Holms- you're up a gum tree, mate!

YOU clearly knew nothing about contactors as you argued their use as an isolator was wrong.

WE clearly did know about contactors as we knew they could.

:lol: :lol: :lol:
 
So as you've all run out of reasons why I'm wrong and refuse to directly answer the points I have raised, except for something in the 17th edition.

Can one of you explain how these contactors work? and why they are a safe form of isolation?

Well, go on then tell me all about them. I won't be holding my breath.
Maybe we've all misunderstood.

Are you actually saying that you don't know what a contactor is, that you don't know how they work?

I have previously explained that the BS for these contactors does'nt exist, but that inconvenient point seems to escape you.
No - what you said was
I checked bs 60947-4-1 on the bs website, there is a section headed "contactors for use as isolators" or words to that effect, and it says "under consideration"
You have not provided any more information about the context of that term - as I observed how are we to know that it's not from a document which said that it's the use of contactors to 60947-4-1 for isolation that is under consideration, not the actual standard itself? You've not said what the date of that document is, or when it was last updated. Maybe when it was written the use of contactors was under consideration - by the committee responsible for BS 7671, and maybe whoever wrote that document has not updated it to take account of the fact that the use is no longer just "under consideration".

Or how do we know that it's not a document referring to a new version of, or an amendment to BS EN 60947-4-1?

We'll never know unless you clarify.

But one thing we do know, is that as the BSI themselves will happily take my money in return for a hard copy of BS EN 60947-4-1:1992 or BS EN 60947-4-1:2001, your claim that "the BS for these contactors does'nt exist", is, to coin a phrase, b*******.

And what's particularly appalling about that is that as you are a subscriber to the BS site you must have known that, since even the most cursory search turns up the fact that there was a BS EN 60947-4-1:1992 and there is a BS EN 60947-4-1:2001, but you decided you'd try and lie to us in order to shore up your crumbling position.

So as BAS has decided to restart this post,
No - I think you'll find you restarted it when without any justification you asserted that at least 7 people contributing to this thread knew nothing about contactors and still don't.

What are these contactors called?
They are called contactors. Maybe some makers call them "isolating contactors" - I don't know. I expect some of them have really boring names like "Contactor 3 poles 15KW 400VAC AC3".

Where can I buy one.
I imagine they are widely available from companies that supply switchgear and controls etc. I expect that the major manufacturers of distribution board components and industrial automation products feature them in their product ranges and that they would be available from the same wholesalers and agents as their MCBs, RCDs, RCBOs, switches, timers, PLCs, busbars, enclosures and so on.

Where do you normally buy things like that? Have you asked there if they sell contactors?

Bas don't be boring and repeat your previous nonsense, just answer my questions - bot of course you cannot can you? :lol: :lol: :lol: :lol: :lol: :lol: :lol: :lol: :lol:
It seems that I can.
 
WF sell contactors that comply with IEC947-4-1.

AL3556, AL3557, AL3558 and AL3559.
 
A contactor is an automatic device, because when a voltage is applied to the coil it starts an automatic process. Voltage flows in the coil, the coil then causes a magnetic field to develop in the plunger, the plunger moves, compressing a spring, and the contacts close. A five stage automatic process, if any part of that process fails the contactor will not close.

But as you probably know BS EN 60947-4-1 has very little to say regarding with the closing of a contactor but it has a lot to say about the opening of the device and the contact spacing.
 
None of those are suitable for use as means of isolation.
How do you know? Not saying you're wrong, just curious to know how you know?

Why don't you give up - before you look for something you have to know what you are looking for.
What are you hoping to achieve here?

We've already shown that EN 60947-4-1 does exist, despite what you said.

We've already shown that BS 7671 explicitly states that some contactors to EN 60947-4-1 may be used for isolation, despite what you think.

Do you intend to use the fact that nobody can tell you where to buy one as proof that the BSI website doesn't actually have copies of the standard for sale, and that there is no mention of them in BS 7671?

I can't tell you where you can buy an AK-47 either, but I know they exist.
 
Funny thing is, as previously stated, I now know what these special contactors are and also realised that I've been installing and commissioning them for years - it's just that in the 17th edition they have
decided to give them a misleading name.

So why did you not look this up in the first place? The fact you had to ask AND that you have been installing and commissioning these 'special' contactors for years without even realising it makes you sound rather foolish.
 
None of those are suitable for use as means of isolation.
How do you know? Not saying you're wrong, just curious to know how you know?

Because I've taken the trouble the trouble to find out!
OK.

What are you hoping to achieve here?

Ah, poor old BAS, up against some one who does'nt give in to his browbeating.
¿Que?

We've already shown that EN 60947-4-1 does exist, despite what you said.

I never said it did'nt exist, what I told you was the part that mentions "contactors for use as isolators" does'nt exist and it does'nt.
BS EN 60947-4-1:2001

Switchgear, Electrical equipment, Electric control equipment, Low-voltage equipment, Low voltage, Electromechanical devices, Electrically-operated devices, Contactors, Electric starters, Protected electrical equipment
.

And BS 7671 says that contactors to that standard with the correct marking may be used as isolators.

I wonder why it would do that if the standard for contactors for use as isolators did not exist?

You still have not clarified the context of the phrase "under consideration".


We've already shown that BS 7671 explicitly states that some contactors to EN 60947-4-1 may be used for isolation, despite what you think.

I'd already accepted that point.
I wonder why it would do that if the standard for contactors for use as isolators did not exist?

Funny thing is, as previously stated, I now know what these special contactors are and also realised that I've been installing and commissioning them for years
A contactor does not constitute and should not be used as a means of local isolation.
A contactor can be used as a means of emergency isolation, but it cannot be used as a form of isolation in accordance with 640.
DP, Ive clearly explained why your proposal does not comply with the regs. You are creating a potentially and needlessly dangerous situation.
 