Cutting padstone

Discussion in 'Building' started by xdrive, 18 May 2020.

  1. xdrive

    xdrive

    Joined:
    2 Mar 2019
    Messages:
    158
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi.

    Putting 203x102x23kg beam at 4m length to open up dining.

    I went to builders merchant for padstone. Only had 440x215x100 size.

    I've cut it in half but now thinking maybe should have used full to spread load.

    Not specified on drawings. From your experience is this OK?

    IMG_20200518_183939.jpg
     
  2. Sponsored Links
  3. noseall

    noseall

    Joined:
    2 Feb 2006
    Messages:
    38,158
    Thanks Received:
    2,447
    Location:
    Staffordshire
    Country:
    United Kingdom
    Did the S.E. specify a padstone size? Did the SE know you had brickwork masonry as opposed to softer blocks?
     
  4. xdrive

    xdrive

    Joined:
    2 Mar 2019
    Messages:
    158
    Thanks Received:
    0
    Country:
    United Kingdom
    No. It was done from drawings.

    Brick is bloody strong. Do I even need padstone
     
  5. tony1851

    tony1851

    Joined:
    23 Feb 2012
    Messages:
    9,581
    Thanks Received:
    1,429
    Location:
    Manchester
    Country:
    United Kingdom
    Have you had any calcs done for this? If so, it would be possible to do a check knowing what load the beam is carrying.
     
  6. Sponsored Links
  7. bennymultifinish

    bennymultifinish

    Joined:
    21 Apr 2020
    Messages:
    620
    Thanks Received:
    106
    Country:
    United Kingdom
    whats in the picture wouldn’t be enough for me. the mortar in the brickwork is soft. i’d use 2 courses of 600mm concrete lintels to spread the load wider.
     
  8. tony1851

    tony1851

    Joined:
    23 Feb 2012
    Messages:
    9,581
    Thanks Received:
    1,429
    Location:
    Manchester
    Country:
    United Kingdom
    That would be overkill for the sort of load the beam would be carrying.
     
    Last edited: 19 May 2020
  9. xdrive

    xdrive

    Joined:
    2 Mar 2019
    Messages:
    158
    Thanks Received:
    0
    Country:
    United Kingdom
    Is only supporting a free standing brick wall and as a purlin for joists.

    Mortor is soft though.
     
  10. xdrive

    xdrive

    Joined:
    2 Mar 2019
    Messages:
    158
    Thanks Received:
    0
    Country:
    United Kingdom
    Pics of end result. Will need to fix brick work in between joists that had dropped down. Other than that job went quite smoothly
     

    Attached Files:

    • Like Like x 1