Hi, I measured the Hot water at the Bath tap fully open just now and it's 3L per 15 secs so that's 12L per min. Sounds about right give-or-take.
Is your boiler 24 or 28kW model?
I suspect 24kW
Hi, I measured the Hot water at the Bath tap fully open just now and it's 3L per 15 secs so that's 12L per min. Sounds about right give-or-take.
Billm, would need to check again but I think flow rate outed for the 28kW might be a stretch at what is pecified for micro genus 28. Your few rate is tad high I think, hence you see 60 degrees
Aware your boiler is not a microgenus, but there should be little difference
Reduce th flow rate a little and le th boiler boils to 70, then check ho water temperature
Very old iPad that gets used when current has been press ganged by SWMBOGremlins in your keyboard @DP?
Billm, would need to check again but I think flow rate outed for the 28kW might be a stretch at what is pecified for micro genus 28. Your few rate is tad high I think, hence you see 60 degrees
Aware your boiler is not a microgenus, but there should be little difference
Reduce the flow rate a little and let the boiler stabilise to 70, then check hot water at the tap
Are you actually measuring the temp coming out of the tap and its 60 degrees?
Billm, would need to check again but I think flow rate outed for the 28kW might be a stretch at what is pecified for micro genus 28. Your few rate is tad high I think, hence you see 60 degrees
Aware your boiler is not a microgenus, but there should be little difference
Reduce the flow rate a little and let the boiler stabilise to 70, then check hot water at the tap
It's still showing 60 on the led's. I assumed the boiler thermostat would restrict it to 60?Billm, it would seem that little bit extra water flowing through the heat exchanger was not quite attaining the 35 degree C specified in the manual
Slowing the water a tad now will show temperature of 70 (if higher adjust for 70). Try the hot water rate measurement again- should be closer to what the manual says.
It's still showing 60 on the led's. I assumed the boiler thermostat would restrict it to 60?