When I used to carry out inspections, I would say dodgy rings were the single most common fault, some caused by NICEIC firms too
My own experience is completely at odds with that, though I have little in domestic environments.
When I used to carry out inspections, I would say dodgy rings were the single most common fault, some caused by NICEIC firms too
Me neither commercial/industrial are my fieldsMy own experience is completely at odds with that, though I have little in domestic environments.
True - but, for new circuits (or when re-wiring), and as you go on to imply, only because people are seemingly 'obsessed' with 2.5mm² cable. In term of Zs and VD, 4mm² is 'almost as good as 5mm² (2 x 2.5mm²) - and, for what it's worth, I personally find 4mm² cable nicer/easier to work with than 2.5mm².To keep within volt drop rules with 2.5 mm² cable with a 25 amp MCB one is limited to around 25 meters, with same 2.5 mm² looking at 106 meters for a ring, so often you can't simply turn a ring final into two radials, and comply with volt drop.
Yes, as I often say, 'CPC redundancy' seems to be the one (and I think probably 'only') thing to be said in favour of ring finals.I like rings because if there is one unregonised break in the earth wires, at least all the sockets will still have an earth.
Probably only 'fractionally' - in the right circumstances, 120V is plenty high enough to kill, and being 'apparently safer' (than 230/240V) may result in a degree of foolish complacency.Probably safer than 230
Indeed - certainly not necessarily.Plus of course - a radial is not simply one line of cable.
Indeed so.Numerous unfused spurs with more than one socket can be installed (plus afterthoughts at a later date) such that a single 25m. limit (if that is what the figure is) to meet Zs maximum can easily add up to considerably more than 25m. with none of the hassle of a ring circuit meandering to - and from - all points.
The USA spec house I lived in this country has both UK mains ring and USA socket outletsThree Don't forget the US has 120v and needs two phases for the larger current appliances.
Intuitively, that sounds like good sense.I do think the 110v outlets and portable household electric 'toys' is the most sensible thing the USA does and I'd support the same in the country.
So let's improve the standard of workmanship and do it properly. And for heavens sake let's do away with the idiot 'electricians' who constanly post their rubbish on social media too.Thats the problem, many are not properly installed or maintained, who is Slep?
In which case it's not USA specThe USA spec house I lived in this country has both UK mains ring and USA socket outlets
The 110volt sockets are supplied via a 20Amp transformer centre tapped to earth.
Until last year they were 'legal' in the whole of EU.There are very few countries where "Rings" are legal to install.
One of the idiots on YT seems to think so and seems to make it a 'chestnut' of his.Plus of course - a radial is not simply one line of cable.
Glad to see I'm not the only one to call it 2 phase.They manage, but we manage much better with the ring on 240v. Don't forget the US has 120v and needs two phases for the larger current appliances.
You should already know you're not the only one - as well as myself, you also have BS7671 as company ...Glad to see I'm not the only one to call it 2 phase.