Surely that would be non-compliant as the conductor may only be rated for 20A (62.5%).Of course not, but the conductors are, electrically, in parallel, and the authors of BS7671 seem to have decided that it is acceptable to assume that the shorter conductor may be considered to carry not more than 75% of the total current.
Wasn't the original rule that it should be 66% and then Methods 100 and 102 'fiddled' to allow 2.5mm²?