drafty air vent

Joined
21 Jul 2009
Messages
1,677
Reaction score
89
Location
Derby
Country
United Kingdom
Hello,

Its not really my area, but I was just wondering something out of curosity.

Visited a rental property recently, whilst chatting, the tenant had a bit of a moan.

After a recent gas check, there was a air vent that had its internal cover replaced from a sliding type (is it a hit and miss?) to a fixed type, about 8 or 9 inch square. Now the tenant is complaining of a draft coming in. He asked me if it would be ok to do this that or the other to it. I gave it a shrug and a 'pffft, you not talking to the right guy, sorry' Quietly walked away thinking it was quiet bad, i wonder if theres any compromise?
 
Sponsored Links
sliding type is not allowed as obviously tennant can shut it and it is "permanant" ventilation.You can get an elephants trunk for outside (vent that faces downwards) tos stop the draught blowing straight in but to be fair there will always be a draught
 
Hi mate,

If the tenant has a flueless gas fire which is 8kW or more, then the air vent is mandatory, and should not be covered or blocked up in anyway.
 
Hi mate,

If the tenant has a flueless gas fire which is 8kW or more, then the air vent is mandatory, and should not be covered or blocked up in anyway.
 
Sponsored Links
There are combustion vents available which have internal baffles or a membrane to allow continuous ventilation with reduced direct air-flow. Not quite draught-free, but as near as possible. An external hood will also help
 
There are combustion vents available which have internal baffles or a membrane to allow continuous ventilation with reduced direct air-flow. Not quite draught-free, but as near as possible. An external hood will also help

good point,the first time i saw one of those i thought someone had blocked the vent because i couldnt see daylight through it.Cut around the caulk took it off and ooops :oops:
 
Hi mate,

If the tenant has a flueless gas fire which is 8kW or more, then the air vent is mandatory, and should not be covered or blocked up in anyway.

Flueless -- 100cm2 mandatory
Open flue appliance over 7kw -- mandatory 5cm2 per kw over 7
Decorative gas fire -- 100 cm2 mandatory, unless specified otherwise in Mi's
 
Hi guys,

Thanks for the info.

I had a word with the landlord about baffled and/or elephant trunk vents and left it at that. If I ever go back there, ill let you know if owt happened about it
 
Hi guys,

Thanks for the info.

I had a word with the landlord about baffled and/or elephant trunk vents and left it at that. If I ever go back there, ill let you know if owt happened about it

i will save you the bother of answering what happened, HE-HAW thats what will have happened, no landlord is going to change a cheap straight through vent for a baffle vent just cause the tenant was getting a draught, as long as the tanants have been advised not to block it then the landlord wont spend a penny fitting a better vent
 
lol, you may be right. Although, to be fair, this chap is one of the more conscientious landlords i've worked for.

Still, i'm not going to put any money on it ;)

thanks anyway :)
 