H
holmslaw
..
The pipe work was not bonded and the customer complained about getting shocks. They got the pipes bonded and all was fine.
OOI, does the same apply if you use DI cable, or put it in conduit?For Electric cables Separation of at least 25mm to be provided for domestic gas pipework up to 35mm....For pipework over 35mm then 50mm of separation is needed.
It's not an earth; it is a bond because the pipe is earthed.I have just been having this debate about strapping the earth to the gas pipe
543.3.1 does not say that. Did you quote the correct number?and was given the following reason for not doing it. Reg 543.3.1 says something about the earth protection/bonding wire not being mechanically supported by the service it is protecting.
We cannot legislate for idiots.This reg is to ensure that a plumber/gas man in re-routing the gas (or water) service pipe does not cut the wire attached to it.
Why would that be desirable?By having an independent route for the earth wire from source (<600 mm inside boundary) to the main earth terminal one disassociates the wire from the pipe;
Unless at point of connection.so any pipe work changes should not cause a change to the continuity of the earth wire.
Quite.This regulation is about protecting the earth wire (not protecting the gas pipe). Of course there is nothing to stop a builder chopping and independently routed earth wire but that is another issue.
Except that this wire is connected to the pipe.However from a gas pipe protection point of view other regulations say that all wires that carry a current should be not less the 25 mm apart from a <=28 mm gas pipe (35 mm for larger pipe) without a second insulating barrier between the pipe and wire. This is to prevent any risk of a spark or shock hazard between wire and pipe.
There can in a fault be current in the bond (don't keep calling it earth).But one might say that there will be no current flow in the earth wire as it is essentially earth potential running alongside the pipe making it safer then a separated wire would be.
Correct.But the logic behind a wire that is making extraneous points at equal potential is that they do it by pulling any voltage difference down to the same value i.e. if a water pipe earth, gas pipe entry and supply earth were at different potentials then they are shorted together by the bonding wire to make the same potential.
No, there would be potential difference and current could flow through you if you touched two of them.This implies that if there was an earth potential difference then some current must flow in the bonding wires to equalise that potential between all extraneous earth points and the MET.
Then there is a fault somewhere.Normally this is unlikely but I recently received a report of an instance of quite high earth bond wire current.
But they are all connected together for that very purpose.Interesting I thought. Maybe further justification for keeping the earth wire wire away from the gas pipe and a reason to have separate wires for MET to each extraneous entry point.
Ah, 5.2.3 of GN8 does say that and refer to 543.3.1 which does not.[543.3.1 does not say that. Did you quote the correct number?]
Okay I was just doing a cut and paste from the report so it is their words not necessarily the regs literatum. The words were:
'Main bonding conductors should not be supported by the service pipes they are connected to,Reg 543.3.1'.
That might be a Guidance Notes 8 or similar interpretation from a gas board document. But it is about protecting the 'protective' wire.
Well possibly but what about where the wire did run?I agree but it is reasonable to assume that if a protective wire is detached from a pipe then anyone working on the pipe won't affect the wire. So it could be a good bit of advice...
We do not put it there to avoid pipe rework .[Unless at point of connection.]
True. But as there has eventually to be a point of termination it is reasonable to put that as close to the service entry to the building to minimise any affect during pipe run rework.
The 600mm. only applies to indoor meters.Also at <600 mm
You have more faith than I.it is more reasonable to assume that only a fully qualified a professional worker will be doing the work and that they will understand the need for the protective wire. Plus inspectors are more likely to see a missing termination but not notice a break in the run or the protective wire.
Mmmm. Yes - to avoid damage but people can avoid damaging them and, as above, what about avoiding damage where they are subsequently placed?[Except that this wire is connected to the pipe.]
I agree, this is just one of those interpretations of the reg 528.3.3 & .4 - 'proximity to non-electrical services'. The On Site Guide says that distribution cables (i.e. cables carrying a working current) should be separated by the quoted distances.
I presume these are your words and not a continuation of the above.If the protective bond wire is carrying current should this also be separated?
There can be no potential difference on a negligible impedance connection.[There can in a fault be current in the bond (don't keep calling it earth).]
Is that only the case for a fault condition? If the logic of the bond wire is that it is making extraneous earth points be at equal potential by bonding (or shorting) them together with a low resistance wire then they must do this by pulling any voltage difference down to the same value. So if there were differences in potential there must be current.
There could be without the bonding. That is why it is applied - to remove it.If there are no differences ever then there is no need for a protective bond wire.
As above, apart from very small earth leakage current - no.The question is can we have a valid reason for a potential difference without there being a fault condition?
No, it (the potential difference) has been removed[No, there would be potential difference and current could flow through you if you touched two of them. That is why they are bonded to remove the difference.]
So ipso facto current must flow through the protective bonding wire which is what the engineer reported to me.
Not if bonded. That is the point.[Then there is a fault somewhere.]
But is it a fault. It is reasonable for the neutral line voltage to rise up from ground earth under load (and the live line to drop a bit). So if the neutral was the house MET (as in TN-C-S) then one could have a neutral and supply earth with a higher potential then a ground earth (e.g. water pipe). This is not a fault condition provided the earth loop resistance and supply voltage drop are within limits.
I don't think that is the reasoning behind the spacing.[You seem to worry a lot about sparks; do you think the gas in the pipe is going to explode?]
I am trying to compare the thoughts that distribution wires are kept away from a gas pipe but a protective bond wire carrying current legitimately need not be. Certainly if something severed a gas pipe and, at the same time, any clipped protective bond wire that carried a current due to earth potential difference then gas could be released at the same place as the severed wire may spark.
The advised spacing with live wires is so little anyway I think the bonding wire is unimportant in this respect.That was my thinking as to why it may be advisable to run the protective bond wire elsewhere to the gas pipe run.
No, it (the potential difference) has been removed[No, there would be potential difference and current could flow through you if you touched two of them. That is why they are bonded to remove the difference.]
So ipso facto current must flow through the protective bonding wire which is what the engineer reported to me.
No, it (the potential difference) has been removed[No, there would be potential difference and current could flow through you if you touched two of them. That is why they are bonded to remove the difference.]
So ipso facto current must flow through the protective bonding wire which is what the engineer reported to me.
If there was potential between pipe and MET before the bond was added then there will still be a potential after the bond is added but it will be reduced to a very low, near zero difference. There will be current flowing in the bond. The potential and current will depend on the impedance between the pipe and the source of the extraneous potential and it ratio to the impedance of the bond cable.
In most cases the impedance of the extraneous source is several tens of ohms or more and the bond is less than a ohm so the potential is to all practical purposes zero,
But were the extraneous source is very low impedance, as in a metallic water main, the ratio allows for a significant voltage and hence a significant current.
In cases where the MET voltage rises due to an elevated neutral potential and the bond is to a water pipe connected to a metallic mains then the current in the bond can be several amps.