IP4X and IP2X is an non-conformity and action must be taken.Thanks. That's what I would have expected. However, of the things you mention, I think that only the metal lights without CPCs and the damaged light accessories (if sufficiently damaged) would get close to qualifying as the 'seriously hazardous problems' I was talking of.
Goes down as a C1 on my reports.
In (Test 1) I have only just just done the the EICR, the house is empty being prepared for the rental, market. So still awaiting the owners instructions to do further investigations. But from what I have seen the wall in the front room has been recently plastered, so could be buried joint in wall or damp in to accessory on RFC.Interesting. What was the cause of the two IR problems?
The garage distribution circuit runs in T&E under the house, leaves property outside to a small flagged area ( cable under flags) in SWA then in to garage. The circuit within garage when disconnected from distribution is fine. So could be damp in junction under floor or damaged cable!
One of the flags that the cable runs beneath is broken in two, so not sure how deep the cable is buried.
(Test 3) Down to lighting circuit insulation being absolutely shot!
I have found 4 IR issues in the last 6 houses I have been to. Normally where the previous owner liked doing a bit of DIY!Is finding IR problems in 2/3 consecutive EICRs 'usual', or was this a bit unusual?