In theory a larger fuse is required and would avoid the overheating.or put a bigger fuse in the fuse box.
In reality it may not be possible as the fusebox may not be suitable for fuses larger than 30A.
Indeed, since I doubt that 33.3A or 35.4A through a 30A fuse would bring about any melting.Although the OP says it gets hot while in use, the 'melting' he quotes could be historic.
Indeed One of our flats had a 7KW shower on 30A and 4mm², a new tenant decided to up-grade to a 9.5KW, it was found on PIR a whole year later, by then the ends of the cable [all 4] were lovely and crispy and had to be replaced along with the 'melted' CU. But the fuse never blew.Indeed, since I doubt that 33.3A or 35.4A through a 30A fuse would bring about any melting.
Kind Regards, John
And chances are, that newer 8.5KW heater is rated for 230V and when run on 240V would potentially be more like 38A [or 40A at 250V] and still the fuse will not blow.Even worse than. 8.5kW at 240 volts is 35.4 amps.
That's not likely.And chances are, that newer 8.5KW heater is rated for 230V
Depends on it's country of origin. Those that were on 220V do tend to quote at 230V and I fairly regularly find currents higher than predicted for this reason.That's not likely.
They would rather call it 9.26kW @ 240V.
You mean the European union? Well now you mention it...Do you mean bought from dubious sources?
Of course it does, a unit rated for say 10KW at 230V has a predicted current of around 43A but run it on 240V and it will be 10.88KW and 45.3A.It doesn't, of course, alter the 'predicted' or expected current.
The last Gainsborough I checked came out a little high, so either it was rated at 230V or it was a heavier heater than quoted. My present 10.5KW Triton at 243V drew 41A so less than10KW.If you buy a Triton, Mira or Gainsborough shower, the rating is at 240V.
It could be but I have never seen one where only 230V is stated.The last Gainsborough I checked came out a little high, so either it was rated at 230V or it was a heavier heater than quoted.
The resistance of the element will increase with the temperature so I would consider that normal.My present 10.5KW Triton at 243V drew 41A so less than10KW.
If that's true, it's a bit daft (and misleading), isn't it? When one powers up a shower or immersion element, it is only a second or two before it reaches operating temperature, and people will be interested in knowing the power consumption when it is operating, won't they (and not what power it would consume if, hypothetically, it could operate without rising in temperature)?!You should have measured the resistance cold. ... The resistance of the element will increase with the temperature so I would consider that normal. ... I don't think I have ever measured the resistance of a shower element but immersion heater elements are usually near the expected resistance when cold - ~19Ω for 3kW @ 240V.
I certainly agree with the physics of what you said - i.e. that the resistance of an element will be higher, and hence the power (at any particular voltage) will be lower, when the element is 'working' (i.e. hot) than when it is cold.Do you disagree? As it will be less than they expect, they may not be too upset.