electric shower upgrade from 9.5kw to 10.5kw

Discussion in 'Electrics UK' started by hmeah, 12 Mar 2011.

  1. hmeah

    hmeah

    Joined:
    25 Oct 2006
    Messages:
    43
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    My old shower( Triton Opal 9.5kw) has packed in, I have replaced it with a new (Triton Martinique 10.5kw), it works fine for a while and then stops, the switch in the fuse box turns off too, i noticed its got a 32a in the fusebox, is this correct?

    :confused:
     
  2. Sponsored Links
  3. wingcoax

    wingcoax

    Joined:
    1 Mar 2009
    Messages:
    1,948
    Thanks Received:
    158
    Location:
    Blackpool
    Country:
    United Kingdom
    32A would be ok for your old shower BUT not for your new one. The big problem is, WHAT SIZE CABLE DO YOU HAVE? Your old shower was probably on 6.00mm or even 4.00mm. Your new one needs 10.00mm as a minimum with a 45A MCB or RCBO, presuming you do not have RCD protection.
     
  4. planemad

    planemad

    Joined:
    5 Nov 2008
    Messages:
    555
    Thanks Received:
    19
    Country:
    United Kingdom
    9500/230 = 41.3 Amps
    10500/230 = 45.6 Amps

    What size is your cable, that's your problem.

    You have also completed electrical work in a bathroom by installing the new shower not matching the existing.

    This is breaking the law and could be creating a danger to yourself and others.

    If the wire is not the correct size (which I doubt it is as the circuit is protected by a B32) then you are lucky you have a B32 mcb that is tripping and not a FIRE.
     
  5. hmeah

    hmeah

    Joined:
    25 Oct 2006
    Messages:
    43
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    i found it like that when i moved in Nov 2006, shower has worked well until recently

    on the mcb/rcd (not sure which is it) in the fuse box downstairs, it says 'wylex b32' and '32a'
     
  6. hmeah

    hmeah

    Joined:
    25 Oct 2006
    Messages:
    43
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    im not sure about the cabling, it goes from the shower into a brickwall and then outside the bathroom to the wall, where the switch is...

    is it paramount the cabling needs upgrading?
     
  7. planemad

    planemad

    Joined:
    5 Nov 2008
    Messages:
    555
    Thanks Received:
    19
    Country:
    United Kingdom
    So you are also unsure about how the cable is run it could be between some nice flammable material.

    Do yourself a favor and call in an electrician, the mcb tripping is your best friend at the moment.
     
  8. hmeah

    hmeah

    Joined:
    25 Oct 2006
    Messages:
    43
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    i did get an electrician to install it, he said nothing about it, now its tripping, im calling him but phone switched off since yesterday!

    I can see the wires behind the wall, its full of water pipes and bricks, no flammable materials...

    If i changed the mcb downstairs to 45a, would it be okay, other then that i may take it back and get a 9.5kw, its what was installed...
     
  9. planemad

    planemad

    Joined:
    5 Nov 2008
    Messages:
    555
    Thanks Received:
    19
    Country:
    United Kingdom

    Are you having a laugh? from the info you have supplied I doubt an Electrician installed a 10500w electric shower on a 32A MCB.


    DO NOT PUT IN A 45A MCB - Get a qualified electrician to take a look at the circuit and complete remedial work as required.
     
    • Thanks Thanks x 1
  10. Sponsored Links
  11. londonboy

    londonboy

    Joined:
    22 Feb 2009
    Messages:
    1,582
    Thanks Received:
    149
    Location:
    London
    Country:
    United Kingdom
    The 9.5kw was incorrect on a 32a breaker too.

    I very much doubt you will be able to take a used shower back to the store!

    A 45a breaker on a 4/6mm cable will result in a fire.
     
    • Thanks Thanks x 1
  12. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,139
    Thanks Received:
    1,752
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    No and no.

    A 32A MCB is not suitable for the new shower.
    It wasn't suitable for the old shower either.
    Changing the MCB would require that the cable size, length and method of installation are known. Then there is the matter of whether an RCD is fitted, and whether the main protective bonding is the correct size (or even exists).

    There are no DIY solutions to this mess.
     
    • Thanks Thanks x 2
  13. hmeah

    hmeah

    Joined:
    25 Oct 2006
    Messages:
    43
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Thanks for all your info and advice, i will get a proper electrician in to look at it.

    all the best... you are the best!
     
  14. planemad

    planemad

    Joined:
    5 Nov 2008
    Messages:
    555
    Thanks Received:
    19
    Country:
    United Kingdom
    Well Done Sir.

    An electric shower is normally the highest demanding consumer in most households and it pays to ensure that this is installed correctly, can operate safely and disconnect the potential within the right time.

    Hope you get it sorted and I hope we has assisted to prevent what could be a hazard.

    Please post up an outcome once you get the circuit work completed.

    Best Regards
     
  15. Spark123

    Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,841
    Thanks Received:
    474
    Location:
    Cumbria
    Country:
    United Kingdom
    You need to use 240v in your calcs as the manufacturers are still pre 17th edn regs ;)
    (Okay, it is probably a sales ploy)
     
  16. ajrobb

    ajrobb

    Joined:
    23 Jan 2010
    Messages:
    1,656
    Thanks Received:
    163
    Location:
    Sussex
    Country:
    United Kingdom
    Your existing 32 A supply circuit is only good for 7.5 kW.

    An MCB has a thermal element that allows extra current for a while and an electromagnetic element that trips immediately. The more extra current you have, the quicker the MCB trips. An MCB will only trip immediately if there is a short-circuit or similar fault (using electromagnetic element). (Lighting circuit MCBs sometimes trip when a light bulb blows as the current gets very high for a split second.)

    A 32 A MCB might pass 40 A indefinitely and 45 A for between 1 and 20 minutes. The plastic cable insulation gets hotter and hotter. If a mistake was made during or since the installation (like loft insulation put against the cable), portions of the insulation could melt!
     
  17. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page