Electrics in bathroom

Joined
14 Mar 2007
Messages
136
Reaction score
0
Location
Yorkshire
Country
United Kingdom
I note that regs state:

Standard electrical wall fittings (such as wall sockets, flexible cord outlets and fused switches etc) are not IP rated so cannot be installed within zones 0, 1 or 2. No standard socket outlets are allowed within 3m of the outer limit of zone 1, and any socket fitted would be on a RCD protected circuit

So although standard sockets cannot be installed within 3m of zone 1, can anyone clarify that it would be OK to install a FCU that is well outside zone 2 but within 3m of zone 1?

Or, although not conventional could a waterproof socket (such as a Masterseal) be used outside zone 2?
 
I don't think 3m reg is to do with the IP rating of the socket - more to do with what people are likely to be plugging in so no, you shouldn't install a masterseal unless it is over 3m away from Zone 1.
Things like FCUs etc are fine outside the zones.
 
Point taken.

You say FCU's etc, what are the etceteras? Can I put a normal lightswitch on a wall outside of zone 2?
 
There is nothing to say that you cannot put a switch outside the zones if it is suitable for the environment....., and your electrics in the bathroom conform to BS7671(2008).
 
The bathroom is quite large (4mx3m) and the switch would be well away from the bath, shower and sink. Obviously a nice polished chrome switch would look better but would it be safer to have a white plastic switch?
 
Why should it matter? If its metal fitting then the front plate must be earthed.

Don't forget that all circuits into the bathroom must now be RCD protected so that will provide supplementary protection.
 
I note that regs state:

Standard electrical wall fittings (such as wall sockets, flexible cord outlets and fused switches etc) are not IP rated so cannot be installed within zones 0, 1 or 2.

The manufacturers will give you the IP rating of equipment; the regs state no such thing.

If you do have a copy then read section 701 and all should be absolutely clear.

Naturally you will also heed all the requirements of part 4, 5 & 6.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top